GRP Firewater Pipe System?
GRP Firewater Pipe System?
(OP)
I have taken over for a large civil project and my predecessor specified GRP/ Epoxy for the seawater firefighting system.
This was to be a wet system and GRP was accepted. The system is now to be a "dry" system with the pumps only running after operator initiation.
Does GRP/ Epoxy have a two hour fire rating if it is a dry system?
All help appreciated, thanks in advance
This was to be a wet system and GRP was accepted. The system is now to be a "dry" system with the pumps only running after operator initiation.
Does GRP/ Epoxy have a two hour fire rating if it is a dry system?
All help appreciated, thanks in advance





RE: GRP Firewater Pipe System?
RE: GRP Firewater Pipe System?
Are there any regulations that need to be met (e.g. IMO, coast guard, etc.), or is this a self imposed requirement?
In addition to the intumescent, you can go to a chartek coating, but the cost and weight will roughly double.
There are FRP systems (e.g. Fiberbond.com) which have been designed to 5 minutes dry 25 minutes of flowing water without passive fire protection (chartek, intumescent), but 2 hours dry without flowing water will most likely not be fesible.
RE: GRP Firewater Pipe System?
RE: GRP Firewater Pipe System?
The best firewater systems that I have seen are loaded and maintained with an electric jockey pump. If the pressure drops below a setpoint (as in someone opens the hose), then the diesel powered firewater pumps automatically startup. It takes one crucical step out of a critical situation.
The US coast guard which regulates floating Oil platforms (TLP, Spar, etc.) have accepted FRP loaded firewater systems that meat IMO Level III firetesting. For the deluge portion, it must meet a 5 minute dry 25 minute flowing water.
The Navy Tested Cu/Ni piping in a dry then wet deluge piping and had a catastrophic failure when the water flashed to steam when it was introduced to the cherry red hot pipe. It believe it was partially based on this that the coast guard moved to accept FRP in dry/wet situations.
Has the customer proposed a test protocol. In some cases only a section of pipe is tested. A problem that I have seen in the past is the jointed conections in a fire test. The gasket selected, may not be able to handle the test.
What is the regulatory body that governs the location of this platform?
RE: GRP Firewater Pipe System?
RE: GRP Firewater Pipe System?
Thanks
RE: GRP Firewater Pipe System?
Steve Jones
Petroleum Development Oman LLC
Muscat
Sultanate Of Oman
RE: GRP Firewater Pipe System?