Floor Loading

Floor Loading

Floor Loading

(OP)
I am trying to determine if there is a standard methodology for calculating floor loading for heavy machinery? I have a 3832 lb gantry to be supported on a concrete floor in a hospital. The gantry is mounted on 4 vibration isolation pads. The two front pads have a 4.5" diameter surface contact (15.9 in^2), and the two rear pads have a 3.5" diameter surface contact (9.6 in^2). The front two pads take 1556 lbs each, and the rear pads take 360 lbs each. The total area under the outer edges of the foot pads is 30" x 56" = 1680 in^2 = 11.67 ft^2.

How do I calculate the floor load spec for the gantry?

Is it the total weight divided by the area under the outside edges of the foot pads? 3832 lbs / 11.67 ft^2 = 328.6 lbs/ft^2?

Is it the max point load from each foot pad? 1556 lbs/15.9 in^2 = 97.86 lbs/in^2 = 14092 lbs/ft^2? (this seems insanely high).

The only floor load specification calculation example that I have is from an IBM site preparation manual that uses service load and static load areas, as well as live load and static load constants.

Any suggestions would be appreciated.

Thanks

RE: Floor Loading

In my view, you design the general floor for the loads that to its use correspond + the loads coming from the gantry. If the gantry loads include the effects of imapc etc, the gantry is portraited as 4 point loads for the gneral structural model. This done, it is always sound practice to put something of substance under point loads. A full section of slab can be right, and also beams of proper strength. This is far better than letting fall the load anywhere in a floor built who knows in what way.

By using the general load for the use the room will be reutilizable when the gantry is someday in the future dismantled.

Respect the supports of the gantry themselves one needs to care the slab has enough shear punch capacity, what you may do as per the applicable code. To all other effects representing the loads as point loads will be enough.

RE: Floor Loading

addernoir,
I believe the equation you are looking for and one that can be used to determine loading (in this case compressive loads) is:

P = Af

where:

P = load, (lb)

A = cross-sectional area (normal to load) for tensile or compressive forces, or contact area for bearing loads (in^2)

f = tensile, compressive, shearing or bearing unit stress (psi)

A bearing point of 15.9 in^2 on a concrete slab 3,000 psi = 47,700 lbs. 14,092 lbs does not seem much.

RE: Floor Loading

Use the concentrated load from each pad to determined size of beams.  The concentrated loads must include the effect of the maximum overturning moment which in all likely hood will result in an uplift effect on the rear pads unless measures are taken to counterbalance or resist the overturning moment.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

eBook - Integrating the Engineering Ecosystem
Aras Innovator provides multiple options for integrating data between systems, depending on the scenario. Utilizing the right approach to meet specific business requirements is vital. These needs range from authoring tools, federating data from various and dissimilar databases, and triggering processes and workflows. Download Now
Research Report - Simulation-Driven Design for SOLIDWORKS Users
In this engineering.com research report, we discuss the rising role of simulation and the paradigm shift commonly called the democratization of simulation. In particular, we focus on how SOLIDWORKS users can take advantage of simulation-driven design through two analysis tools: SOLIDWORKS Simulation and 3DEXPERIENCE WORKS. Download Now
White Paper - Industry 4.0 and the Future of Engineering Education
With industries becoming more automated, more tech-driven and more complex, engineers need to keep their skills and knowledge up to date in order to stay on top of this wave—and to be prepared for the Industry 4.0 future. The University of Cincinnati offers two online Master of Engineering degree programs designed specifically for practicing engineers. Download Now
eBook - The Design Gridlock Manifesto
In this eBook, you’ll learn 6 ways old CAD technology slows your company down and hear how design teams have put those problems to rest. “The Design Gridlock Manifesto” shares first-hand modern CAD experiences from 15 companies around the world. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close