I have a question on conduit. In  the plant where I work we have lots of Rigid (RMC) and EMT of different sizes. I see in books IMC. I'm wondering when or where is IMC used ? Is it a protection issue or a expence issue ? Does IMC use threadless fittings like EMT ?
Thanks
Replies continue below

Recommended for you

RE: IMC

The I in IMC is intermediate, not rigid but not EMT.  It uses fittings like rigid conduit but has reduced wall thickness.  Personally I think it works well for most industrial environments, the exception being extremely harsh chemical environments where even rigid should have a PVC jacket.

RE: IMC

At most industrial (and even commercial) installations I've seen, IMC is generally not used.  They either select EMT for light duty, or RGS (rigid galvanized steel) for heavy duty.  The philosophy being that if the environment is abusive enough to warrent IMC or RGS, they might as well put in RGS, given the relatively low difference in cost of IMC and RGS.  RGS will withstand a blow from the proverbial fork-truck much better than IMC.

So far as I know, NEC treats IMC and RGS essentially interchangeably, whereever one is permitted, the other is OK too.  I'm pretty sure that even applies to hazardous explosive installations (although you might wanna double check that).  

So all in all, it really comes down to your environment, your personal preference, and your budget.

Beware, lots of IMC is aluminum -- obviously, if you're in concrete, you don't want any aluminum.

RE: IMC


A frustration can be that some IMC requires installation tooling that is slightly modified/optimized/adjusted compared to that for GRC.
  

RE: IMC

By the way, at the other extreme, I know of at least one manufacturing site that runs all their 5kV lines through EMT, unless they absolutely positively have to put in something more substantial.

RE: IMC

I have run all three and prefer the IMC because of the strength and ease of bending compared to rigid.  It also tends to have a better surface finish than rigid.

Barry

RE: IMC

Barry,
   I have had the opposite experience with IMC, but it was a number of years ago.  It seems harder to bend than rigid because the steel itself is harder, and we had trouble with the  conduit breaking at the threads in the sizes under 1".  The wall thickness of IMC is less than rigid and when you thread it  there is not much strength left at the threads.
Don

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close