I have a question on conduit. In the plant where I work we have lots of Rigid (RMC) and EMT of different sizes. I see in books IMC. I'm wondering when or where is IMC used ? Is it a protection issue or a expence issue ? Does IMC use threadless fittings like EMT ?
Thanks
Thanks
RE: IMC
It may be appropriate to compare products from manufacturers of all three.
http://www.alliedtube.com/html/ecd.htm
http://www.westerntube.com/conduit.htm
http://www.republic-conduit.com/flash/
RE: IMC
RE: IMC
So far as I know, NEC treats IMC and RGS essentially interchangeably, whereever one is permitted, the other is OK too. I'm pretty sure that even applies to hazardous explosive installations (although you might wanna double check that).
So all in all, it really comes down to your environment, your personal preference, and your budget.
Beware, lots of IMC is aluminum -- obviously, if you're in concrete, you don't want any aluminum.
RE: IMC
A frustration can be that some IMC requires installation tooling that is slightly modified/optimized/adjusted compared to that for GRC.
RE: IMC
RE: IMC
Barry
RE: IMC
I have had the opposite experience with IMC, but it was a number of years ago. It seems harder to bend than rigid because the steel itself is harder, and we had trouble with the conduit breaking at the threads in the sizes under 1". The wall thickness of IMC is less than rigid and when you thread it there is not much strength left at the threads.
Don