electric supply to fire water pump

electric supply to fire water pump

electric supply to fire water pump

(OP)
i have a controlgear rated for 1200A,480v. one of the feeder is a fire water pump.having a FLA of 240A(locked rotor current 1500A Approx. i am extracting the local std requirement for fire pump unit package.
"QUOTE"
The protection schemes for Fire Pump Unit (FPU) packages shall comply with NFPA 20 and NFPA 70.  In general, these standards require that the motor be allowed to operate under locked rotor condition continuously and is only automatically disconnected under short-circuit conditions.
Exception :
    The exception to these requirements is that where a FPU package is fed from a bus that has ground overcurrent protection on the incomers or supply transformers, the feeder to the FPU package shall have ground overcurrent protection, and all other feeders connected to the same buses or transformers shall have ground overcurrent protection.
"UNQUOTE"

my question is will this controlgear be sufficient to supply the locked rotor condition mentioned? does the exception above mean that by providing groung fault protection i do not have to comply with require that the motor be allowed to operate under locked rotor condition continuously. please comment.
Replies continue below

Recommended for you

RE: electric supply to fire water pump

No.  The exception deal with the disconnecting portion of overcurrent protection.  In other words, if you have the ground fault protection, you are 1) required to have it present at all the locations listed, and 2) now allowed to  have the ground fault protection  automatically  disconnect in the ground fault instance and not only in the  short-circuit instance.

With this requirement, the locked rotor "operation" could easily exceed the capabilities of the gear in question,  even without considering the other loads involved.

Consideration should also  be given to emergency requirements for this service.

Also, some locations will allow  you  to have separate service for the  fire pump and associated equipment.

Hope this helps.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close