what loads working or ultimate should be taken in foundation design

what loads working or ultimate should be taken in foundation design

what loads working or ultimate should be taken in foundation design

(OP)
I want to know why working loads are used in case of foundation design while the entire structure is designed on ultimate. whats the reason behind this.

Q-1 .. why the min steel requirement in foundation is 0.81% whats the reason behind this?

Q-1 .. whats steps u recommend when designing a footing size to support loads on 2 columns ( live load = 200 & 300  ,dead load 200 & 100 on both columns respectively ) which are spaced at 30ft clc . allowable soil pressure is 6k/ft.

RE: what loads working or ultimate should be taken in foundation design

In answer to your first query only, I would suggest that foundation design is not really any different from the rest of structural design in regard to the use of 'ultimate' or 'working' loads.

Whether we are designing steel or concrete structures, BOTH types of load need to be considered for most structures.

For load capacity, many (most ?) design codes now specify that you calculate structural strength under ultimate loads and provide some reserve against total collapse.  But that is not all that they require.

Most codes also specify particular limits that apply under 'serviceability' or 'working' conditions.  These may include limits on deflections, crack widths in reinforced concrete (especially for water retaining structures), perhaps zero tension stress in prestressed concrete.

When it comes to the foundations, you have a similar situation.

The reinforced concrete design can be done with ultimate loads, but the permissible bearing pressure can often depend on the maximum acceptable settlement under actual loading, and therefore common practice is to specify it as a 'working' limit.

RE: what loads working or ultimate should be taken in foundation design

Taking the issue from a Geotechnical view point, The actual foundation  and supporting soils tend to 'feel' a fairly light structure. When I have jacked/repaired structures, they are usually 'light', compared to calculated loads. Dead loads are usually overestimated as a whole. It must be recognized that ndividual beams, columns and slabs may experience localized heavier dead loads. The same reasoning is even more apparent with live loads, except for some types of structures ( i.e. Rigid-framed steel structures experiencing wind loads).

As far as the sizing footings, I have seen quite a few criteria, depending on local practices, size of structure/loads and the soil conditions.  Residential and light commercial being a 'horse of a different Merry-go-Round' as compared to heavy, multi-story structures.

The correct methodology would be to perform settlement analysis for diffrent loadings and try to minimize differential settlement. As a start for determining loading combinations I suggest the following.

When dealing with light (5 to 20 k/pad) to medium weight (20 to 50 k/pad) structures, on compressible soils (.8 to 3 k/ft), I typically see DL + 1/2 LL for up to 3 stories  and  DL + 1/3 to 1/4 LL for more than 3 stories. I have seen and used similar criteria for heavier structures on somewhat stronger soils (3 to 5 k/ft).

When dealing with expansive soils, I typically use dead load  to confirm the minimum load condition is met (and I try to stay 20% to 50% above the minimum required, if possible). I check DL + LL for the Maximum Allowable, possibly allowing for a 10% to 20% overload, depending on how good or bad I think the information is.

Looking back on this, it reads like a hydrologist giving his anticipated flows. My Father always said that Hydraulics and Geotechnics is half art. He should have known, He was both.

I hope this helps.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close