Flange Removal

Flange Removal

Flange Removal

(OP)
I have a simple question over an ongoing office debate.  Picture a column with 5" x 0.25" flanges and a 10" web.  If the tension flange was removed and 2 2.5" x 0.25" plates welded to both sides of the web approximately 1" from the web end with 3/16" fillet welds, on the surface you would have similar section properties to the original column.  I believe that in reality you would only have a stiffened T-section and the column would be subject to failure when loaded in bending.  Please help with this office debate and if you have any good examples or references to prove your opinion, please let me know.

RE: Flange Removal

Is the modification a localised modification over a finite distance or along the entire length of the column?  Are the welds on both sides of the 2.5” x 0.25” plates?

If the modification is localised then the designer must ensure the adequate transfer of the flange forces.  Provided the details are suitable at the change from “proper” flange to the “replacement” flange, then my feeling is that you have close to the original section capacity.

We have modified a lot of columns, mainly using flange doubler plates or beam tees to make a cruciform section, and these have been assumed to contribute to the overall section.  

If the existing column is in situ at the time of the modification, then the "tee" section will have some existing stress state.  Perhaps the additional flanges (or other additional stiffening elements) don’t contribute to resisting this stress state, however, as the column become more heavily loaded and approaches the ultimate limit state my feeling is that the combined section will be effective.

What is your technical rationale for assuming the replacement flange does not contribute to axial capacity or bending capacity?

RE: Flange Removal

If you take off the flange and then replace it 1" further towards the center of the web, then you have a different section with different properties.  Instead of a W10, now you have a W9.

RE: Flange Removal

ya... but buckling was likely about the weak axis... <G>

RE: Flange Removal

Bearing different too

RE: Flange Removal

(OP)
A little more information on this discussion.  The flange is removed from the bottom 1/3 of an in-situ column.  The web of the column has also been reduced by approximately 1/3 of the original depth.  In analyzing the column, it will be fine if a flange is added at the edge of the web.  However, given the connection of plate to the side of the web with fillet weld only that are not full penetration, I believe that this would only be a T section with longitudinal stiffeners.  The column would be over designed for weak axis bending, but would be subject to failure when combined axial and bending about the major axis is applied.  I have no justification for my argument other than the fact that no one has yet to convince me otherwise.  If you have a simple example that can prove or disprove my theory, pleaqse share it.

RE: Flange Removal

In the simplified model of an I-beam, the flanges carry all the bending moment and none of the shear while the web carries all of the shear and none of the bending moment.

Calculate the shear flow at the web/flange interface as follows:
v = V x Q / I
   v = longitudinal shear flow
   V = shear force
   Q = first moment of area of flange about neutral axis
   I = second moment of area of section

Thus the flange, whether connected continuously by fillet weld or discretely by bolts or rivets, can be effective if the connecting elements can adequately transfer the shear flow.  Consider the design of plate girders as an example.

Get out your university textbooks or search the Internet if you need to read more about shear flow.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close