EQUIPMENT GROUND CONDUCTORS IN PARALLEL
EQUIPMENT GROUND CONDUCTORS IN PARALLEL
(OP)
THE NATIONAL ELECTRICAL CODE, ARTICLE 250, GROUNDING, PARAGRAPH: 250-122(f),(1): STATES " EACH PARALLEL EQUIPMENT CONDUCTOR SHALL BE SIZED ON THE BASIS OF THE AMPERE RATING OF THE OVERCURRENT DEVICE PROTECTING THE CIRCUIT CONDUCTORS IN THE RACEWAY OR CABLE IN ACCORDANCE WITH TABLE 250-122.
THE APPLICATION OF THIS CRITERIA IS TO PREVENT OVERLOADING AND POSSIBLE BURN-OUT OF THE GROUNDING CONDUCTOR SHOULD A GROUND FAULT OCCURS ALONG ONE OF THE PARALLEL BRANCHES.
HOWEVER, CONSIDERING ALL PARALLEL BRANCHES WILL CONTAIN THE SAME LARGEST SIZED GROUND CONDUCTOR SEEMS A BIT EXCESSIVE WITH REGARDS TO THE TOTAL GROUNDING "CSA" OF THE REST OF THE CONDUCTORS INSTALLED WITHIN THE PARALLEL SETS OF CONDUCTORS.
I WOULD LIKE TO KNOW WHY THE LARGEST GROUND CONDUCTOR SIZE MENTIONED IN TABLE 250-122 "MINIMUM SIZE EQUIPMENT GROUNDING CONDUCTORS FOR GROUNDING RACEWAY AND EQUIPMENT" CAN'T BE PROPORTIONATELY REDUCED IN SIZE SO THAT THE SUM OF ALL THE INDIVIDUAL CONDUCTORS CONTAINED WITHIN THE PARALLEL SET OF FEEDERS WILL EQUAL OR EXCEED THE MINIMUM CONDUCTOR SIZE MENTIONED IN THIS TABLE.
RE: EQUIPMENT GROUND CONDUCTORS IN PARALLEL
Short time withstand rating 28000 amps for 4 cycles. The return path would be 2 1/0 , the impedance would depend upon the location of the ground fault. The idea is to escalate the current as quick as possiable so the OCD will clear the fault. Also recommended for parallel feeder are cable limiters to disconnect the damage cable, and allow operation under limited conditions.
RE: EQUIPMENT GROUND CONDUCTORS IN PARALLEL
HOWEVER, CONSIDERING ALL PARALLEL BRANCHES WILL CONTAIN THE
SAME LARGEST SIZED GROUND CONDUCTOR SEEMS A BIT EXCESSIVE
WITH REGARDS TO THE TOTAL GROUNDING "CSA" OF THE REST OF
THE CONDUCTORS INSTALLED WITHIN THE PARALLEL SETS OF
CONDUCTORS.
Namely, why would all parallel branches contained the same largest sized ground conductor?