ALEVIN
Electrical
- Aug 2, 2000
- 4
THE NATIONAL ELECTRICAL CODE, ARTICLE 250, GROUNDING, PARAGRAPH: 250-122(f),(1): STATES " EACH PARALLEL EQUIPMENT CONDUCTOR SHALL BE SIZED ON THE BASIS OF THE AMPERE RATING OF THE OVERCURRENT DEVICE PROTECTING THE CIRCUIT CONDUCTORS IN THE RACEWAY OR CABLE IN ACCORDANCE WITH TABLE 250-122.
THE APPLICATION OF THIS CRITERIA IS TO PREVENT OVERLOADING AND POSSIBLE BURN-OUT OF THE GROUNDING CONDUCTOR SHOULD A GROUND FAULT OCCURS ALONG ONE OF THE PARALLEL BRANCHES.
HOWEVER, CONSIDERING ALL PARALLEL BRANCHES WILL CONTAIN THE SAME LARGEST SIZED GROUND CONDUCTOR SEEMS A BIT EXCESSIVE WITH REGARDS TO THE TOTAL GROUNDING "CSA" OF THE REST OF THE CONDUCTORS INSTALLED WITHIN THE PARALLEL SETS OF CONDUCTORS.
I WOULD LIKE TO KNOW WHY THE LARGEST GROUND CONDUCTOR SIZE MENTIONED IN TABLE 250-122 "MINIMUM SIZE EQUIPMENT GROUNDING CONDUCTORS FOR GROUNDING RACEWAY AND EQUIPMENT" CAN'T BE PROPORTIONATELY REDUCED IN SIZE SO THAT THE SUM OF ALL THE INDIVIDUAL CONDUCTORS CONTAINED WITHIN THE PARALLEL SET OF FEEDERS WILL EQUAL OR EXCEED THE MINIMUM CONDUCTOR SIZE MENTIONED IN THIS TABLE.