shallow foundation VS shallow foundation !

shallow foundation VS shallow foundation !

shallow foundation VS shallow foundation !

(OP)


#1. is it a good idea to build a two story house with CMU walls and wood 2nd floor and roof trusses on a wall footings that are cast monolythicly with the 4" concrete slab on grade? ( similar to a thickened slab and/or edge )

or

#2. is it better to use the other option which is to cast wall footings first start the stem walls and then cast the slab on grade with premolded joint filler material all around?


please state why you would go with either one of the above options.

Your thoughts are appreciated.

V2

Replies continue below

Recommended for you

RE: shallow foundation VS shallow foundation !

If the wall footer is cast monolithically with the slab on grade, differential settlements may cause the slab to crack.

RE: shallow foundation VS shallow foundation !

For a house, I would not hesitate to use monolithically placed slab with footing granted the footing is adequate for the soil bearing pressure. I would use reabrs and extend them into the slab. This will reinforce the small section of the slab should any settlement takes place.

The monolithic slab-footing has been used very successfully in Florida. I have an old DOS program that designs the footing and the bar size and length into the slab.

Good luck.

RE: shallow foundation VS shallow foundation !

I found some good information on thickened slabs just by searching on Google for "Thickened concrete slab"  there are links to several building departments.  It seems to be a common item for building departments to decide whether they will approve this detail.  It seems prudent to not use a thickened slab under individual column loads or for an addition greater than one story.

Check out this spec from Denver Colorado:
http://www.denvergov.org/Home_Improv_Guides/template31322.asp

This kind of question has a lot of variables best left to a local engineer.  Most engineers fees will be less than the various contractors on-site.

RE: shallow foundation VS shallow foundation !

When I design the thickened footing, I assume it is a grade beam on elastic foundation. I usually make it 16 inches deep and 24 inches wide (MINIMUM!) and of course the steel reinforcement in top and bottom. I use #3 hoops equally spaced.

Butler Foundation manual has an excellent dissertation about this type of footings.

I agree that the use must be left to local engineer. This is always prudent.

RE: shallow foundation VS shallow foundation !

Depth of the footing foundation is usually determined by the soils investigation. If a shallow footing is adequate, I usually go with monolithic, sometimes the soils characteristics will determine a footing depth of say 24 inches or deeper, in this case a stem wall is a better solution.

RE: shallow foundation VS shallow foundation !

(OP)
The project will consist of more than 150 repeated buildings. the footprint of a typical buildings is 150 feet by 52 feet. these buildings are townhouses with a mix of one and two story units. there are concrete columns at the end or midle of reinforced C.M.U. walls that transfer loads from concrete beam above on the second level.

I may sound repeating myself. the big question is this:
is it common to to cast the the first floor slab on grade monolithic with all the footings in one poor with no control joints? this project is in Dade-County Florida.

thank you

V2

RE: shallow foundation VS shallow foundation !

If I read your last post correctly, building has a reinforced concrete frame supporting the second floor and roof, so the footing in question will only carry the weight of one story of cmu.

In southern states, where frost heave is not an issue, a thickened slab should be a fine option for a lightly loaded wall.  However, if left unreinforced, Taro is correct in stating that the slab will crack at the edge of the thickened part.  

I'm assuming that this crack, and the potential differential movement would be unacceptable to the homeowner, therefore, I would recomend providing dowels from the thickened portion into the main slab.  That being said, the slab itself should have a minimum reinforcement, else you run the risk of a crack developing wherever the bars end.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close