I'm running a 300 amp service into a building. No one I talked to can tell me what the branch AIC breaker rating should be. Is there a rule of thumb to use or should I specify 100K to be safe. Right now, I have specified 65K.
Thanks,
striped.bass@erols.com
Thanks,
striped.bass@erols.com
RE: Amps Interrupt Capacity
RE: Amps Interrupt Capacity
RE: Amps Interrupt Capacity
case circuit breakers. IEEE Standard 1015-1997 Table 3-19
states that a individual pole of a 3 pole circuit breaker
800 A Max 480/277 is subjected to 10,000 amp L-N SHORT CIRCUIT CURRENT, notice this is far below the 3 pole rating. Consult the manufacture for the breakers single pole
interrupting rating.
RE: Amps Interrupt Capacity
RE: Amps Interrupt Capacity
1. Electric Utilities have their power distribution system modeled by Power Distribution Analysis software, usually. They may send you a printout and data outlined in a letter. Sometimes, one may interpret it easily, if one is familiar with SKM, Inc. program DAPPER, A_FAULT, or ETAP software computer printouts.
2. Else, you may perform the short circuit analysis by yourself; however, you will still need system impedances, and voltages from the Electric Utility to be on the accurate side.