Hello,
I have a task where I have to check a design of a steel signage structure to be mounted on a 6" thick block masonry wall. The anchor bolts are post installed expansion bolts. I am unable to find a specific code (ACI or any other respective USA code) on this matter. What I found is ACI 318 do talk about anchorage to concrete, but I am not sure if it is applicable to block masonry? Also another code TMS 402 "BUILDING CODE REQUIREMENTS AND SPECIFICATIONS FOR MASONRY STRUCTURES", but this code talks about cast in place anchors only. Please help me out in this regard, refer me to a respective code/book.
I have a task where I have to check a design of a steel signage structure to be mounted on a 6" thick block masonry wall. The anchor bolts are post installed expansion bolts. I am unable to find a specific code (ACI or any other respective USA code) on this matter. What I found is ACI 318 do talk about anchorage to concrete, but I am not sure if it is applicable to block masonry? Also another code TMS 402 "BUILDING CODE REQUIREMENTS AND SPECIFICATIONS FOR MASONRY STRUCTURES", but this code talks about cast in place anchors only. Please help me out in this regard, refer me to a respective code/book.
RE: POST INSTALLED ANCHORS IN BLOCK MASONRY
There are different products for hollow versus fully grouted - and I think that many products are only for use in 8" nominal block.
RE: POST INSTALLED ANCHORS IN BLOCK MASONRY
RE: POST INSTALLED ANCHORS IN BLOCK MASONRY
@jjl317 and EngDM The designer (vendor) is using "Rawlplug" bolts so I tried their software but there is no block masonry option available there. They are only dealing with brick masonry which is not applicable to my case.
Any more help is much appreciated.
RE: POST INSTALLED ANCHORS IN BLOCK MASONRY
RE: POST INSTALLED ANCHORS IN BLOCK MASONRY
You need to look to the manufacturer's literature.
RE: POST INSTALLED ANCHORS IN BLOCK MASONRY
This this this.
I know it isn't directly related, but there was a thread earlier this year (thread507-520923: Shear Wall Hardware Manufacturer Claims ACI 318 Anchorage Requirements Don't Apply) where dealing with manufacturers proprietary products was discussed. If you are forced to use these "Rawlplug" anchors, then the designer should be providing calculations or demonstrating of code compliance. I wouldn't be stamping anything proprietary unless I could recreate the results myself via codified equations, or in the case of tested values, verify that tests were carried out in a code compliant fashion.