Hello, I am working on a design for a 4160V system which is high impedance grounded through an NGR. I'm looking at the design for a voltage transformer which is 4200/120V, wye/wye connected. One of the engineers said they typically leave the primary side of the VT ungrounded, but they ground the secondary side going to the relaying/metering. My concern with this is that if there is a ground fault on the primary side of the VT, the primary side fuse may not blow and you will have higher voltages on the non-faulted phases of the VT which could damage insulation.
RE: Voltage Transformer Wye Ungrounded Pri - Wye Grounded Sec Question
When one this sentence into the German to translate wanted, would one the fact exploit, that the word order and the punctuation already with the German conventions agree.
-- Douglas Hofstadter, Jan 1982
RE: Voltage Transformer Wye Ungrounded Pri - Wye Grounded Sec Question
RE: Voltage Transformer Wye Ungrounded Pri - Wye Grounded Sec Question
If the primary wye point is not connected to the system neutral (usually by grounding) then the secondary voltages may be unbalanced in response to unbalanced secondary loads.
This may not be as bad as a simple analysis may indicate as the effect may be limited by transformer saturation due to over-voltages caused by secondary faults or unbalanced secondary loading..
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Voltage Transformer Wye Ungrounded Pri - Wye Grounded Sec Question
This could be the reason why VT primary star is not grounded, probably.
In Generating stations with HRG of Generator neutral, IEEE recommends grounding of y-phase instead of neutral on VT secondary. The primary neutral is grounded. With this arrangement, secondary ground fault will not be seen as ground fault on primary side of VT.
R Raghunath