What is the current code requirement for any reduction in foundation self-weight (D) when resisting wind uplift (W)?
2021 IBC contains the following verbiage:
"For load combinations that include the counteracting effects of dead and wind loads, only two-thirds of the minimum dead load likely to be in place during a design wind event shall be used."
In spite of this, there is no load combination shown that includes 0.67D.
In ASCE 7-16, combination 7 gives 0.6D + 0.6W. This is different from the two-thirds that IBC says.
2021 IBC contains the following verbiage:
"For load combinations that include the counteracting effects of dead and wind loads, only two-thirds of the minimum dead load likely to be in place during a design wind event shall be used."
In spite of this, there is no load combination shown that includes 0.67D.
In ASCE 7-16, combination 7 gives 0.6D + 0.6W. This is different from the two-thirds that IBC says.
RE: Foundation Self Weight for Resisting Uplift
Either way, I believe the 2/3rd is generally in line with the logic of a 1.5 SF for overturning and such.
RE: Foundation Self Weight for Resisting Uplift
RE: Foundation Self Weight for Resisting Uplift
RE: Foundation Self Weight for Resisting Uplift
www.PeirceEngineering.com
RE: Foundation Self Weight for Resisting Uplift
RE: Foundation Self Weight for Resisting Uplift
www.PeirceEngineering.com
RE: Foundation Self Weight for Resisting Uplift
RE: Foundation Self Weight for Resisting Uplift
This is the first sentence from the code section you quoted:
This entire code section is to be used in lieu of and not with ASCE 7. You either use 1605.1, which directs you to ASCE 7 for the load combinations, or you use 1605.2, which has its own combinations and additional rules to follow. They don't mix.
RE: Foundation Self Weight for Resisting Uplift
RE: Foundation Self Weight for Resisting Uplift
RE: Foundation Self Weight for Resisting Uplift
RE: Foundation Self Weight for Resisting Uplift
RE: Foundation Self Weight for Resisting Uplift
RE: Foundation Self Weight for Resisting Uplift
Right. And are you using ASCE 7 load combinations to do it, or are you using IBC alternative load combinations?
RE: Foundation Self Weight for Resisting Uplift
RE: Foundation Self Weight for Resisting Uplift
If you now use 0.67 dead for the foundation, you have mixed the load combinations, which is no good.
RE: Foundation Self Weight for Resisting Uplift
Also 0.6 vs 0.67 is splitting hairs imho.
RE: Foundation Self Weight for Resisting Uplift
I'll let you explain that to my contractors who are trying to run competitive businesses.
RE: Foundation Self Weight for Resisting Uplift
RE: Foundation Self Weight for Resisting Uplift
"..only two-thirds of the minimum dead load likely to be in place during a design wind event shall be used."
In the alternative combination you shouldn't be using 2/3 of your normal dead load it should only be the dead load you reasonably assume will be there during the design event. In the case of the cast-in-place dead man 2/3 of self weight is likely reasonable. In the case of a building 2/3 of the design superimposed dead load is not likely accurate.
"..wind uplift is provided by truss manufacturer.."
usually no you as the EOR are providing the uplift to the truss manufacturer, they typically aren't figuring out the loads for themselves (some do but I think it's in TPI-1 that all loads should be provided by the EOR)
RE: Foundation Self Weight for Resisting Uplift
While we are required by chapter 16 to provide it, I've found that most truss manufacturers do come up with it themselves. A significant portion of the trusses produced are not used on engineered structures, and so the standard software has a wind module that automatically determines the wind load on a roof truss. I think it's easier for them to just enter the wind speed, building height, and exposure class and get it automatically rather than trying to manually enter the wind loads we provide.