Sychro check relays for short term paralleling
Sychro check relays for short term paralleling
(OP)
In an M-T-M configuration, when performing short-term paralleling (momentary paralleling), is it necessary to have synchro-check relays installed in:
a) The Main Incomers (A & B)?
b) The Tie?
c) Both the Main Incomers and the Tie?
What is the standard practice?
a) The Main Incomers (A & B)?
b) The Tie?
c) Both the Main Incomers and the Tie?
What is the standard practice?
RE: Sychro check relays for short term paralleling
Is there any possibility of an out-of-phase condition developing between the incomers? Many of the industries I dealt with that were connected to feeders 44 kV and below took it on faith that they would never be supplied out of phase and therefore had no synch check facility of any kind, and to the best of my knowledge after 44+ years we as a utility never broke their faith.
In areas where there is grid-connected generation with dual grid-supplied M-T-M facilities the situation is different; there I'd without a doubt go with "c".
CR
"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
RE: Sychro check relays for short term paralleling
The customer installed sync-check.
This is better as that customer now wants to install generation, which will require it.
RE: Sychro check relays for short term paralleling