Earth conductor sizing......

Earth conductor sizing......

Earth conductor sizing......

(OP)
Yes, i know, its been done millions of times before! So sorry in advance.

So, im overthinking this so doubting myself. Opinions please.....

Cable from X to Y - 5km long. Secondary Voltage 11kV (Primary is 66kV, Z=6%). Power 6MW. System is TN-C. The cable is 3 core and earth. Cable conductor size is 240mm2 and copper. I dont have a protection device trip time so assuming 0.7s.
The cable is on the output (secondary) of a Dyn11 transformer. Star point is grounded via a 335ohm resistor. The NER is inbetween the star point and the PEN.

Fault current calculated at 18.9A. NER resistor selected is 25A rating.

Using the adiabiatic equation, the earth conductor is calculated as very small, so referencing IEC 60364-5-54, im going to select the earth core is 10mm2 in the 5km cable.

Comments please.......



Replies continue below

Recommended for you

RE: Earth conductor sizing......

For earthing -protective- conductor cross-section area see BS7671 Regulation 543.1.3.
S=sqrt(I^2*t)/k k=143 see Table 54.3 then S=sqrt(18.9^2*0.7)/143=0.11 mm^2.
But, according to table 54.1 the minimum cross section area of protective conductor has to be 2.5 mm^2[protected against damage] or 16 mm^2 if it is not protected.
In my opinion 2.5 is enough.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close