Circuit Protective Conductor CPC calculation and Design
Circuit Protective Conductor CPC calculation and Design
(OP)
I came across a formula for circuit protective conductors in bS76761 18th edition page 196 which states S=sqrt(12*t)/k
where S is the csa (mm2) of the conductor
I is the fault current
t is the time in seconds for disconnection
k is the factor taking account of coefficient, temperature and the likes
what I don`t understand is which fault current is being talked about here, is it the earth fault?
where S is the csa (mm2) of the conductor
I is the fault current
t is the time in seconds for disconnection
k is the factor taking account of coefficient, temperature and the likes
what I don`t understand is which fault current is being talked about here, is it the earth fault?
RE: Circuit Protective Conductor CPC calculation and Design
RE: Circuit Protective Conductor CPC calculation and Design
RE: Circuit Protective Conductor CPC calculation and Design
For line conductor protection against fault current see Regulation 434.
In this chapter this formula-modified accordingly-is used in order to state the minimum clearing time of fault current.
RE: Circuit Protective Conductor CPC calculation and Design
RE: Circuit Protective Conductor CPC calculation and Design
RE: Circuit Protective Conductor CPC calculation and Design
RE: Circuit Protective Conductor CPC calculation and Design
The standard IEC 60364 [ all the parts] it is only for up to 1000 V a.c. and 1500 V d.c.
In chapter 11 of the part 1 of this standard is written:
11.2 It covers:
a) circuits supplied at nominal voltages up to and including 1 000 V a.c. or 1 500 V d.c.
For medium voltage cables see IEC 60502-2
For high voltage cables see IEC 60840.
For earthing details see BS 7430 and BS-EN-50522
RE: Circuit Protective Conductor CPC calculation and Design
http://at.dii.unipd.it/renato.gobbo/didattica/cors...