Calculating Attenuation of GPR Transfer on OHL Grounds/Buried Grounds
Calculating Attenuation of GPR Transfer on OHL Grounds/Buried Grounds
(OP)
I have read in reports and seen during testing, that substation GPR attenuates as it is transferred out to remote areas that are directly connected (via intentional grounds) to remote facilities. In the testing I witnessed, the substation had a ground fault imposed at a non-60Hz frequency. Step/touch and GPR were measured at a nearby generating system where the gen grid was tied to the substation grid with a couple buried 250MCM bare conductors. GPR was seen to attenuate from that being imposed on the substation grid.
In the case of the reports, the direct connection was over the ground wire on a overhead line out to a mining pit. I have a great deal of faith in the engineer running the tests and writing the reports but he is long since retired to ask questions of. My question is, has anyone ever seen a method for calculating the attenuation of GPR transfer over various types of ground connections?
I am not even certain I understand the mechanism by which it attenuates (capacitive charging current?) to begin coming up with a way to calculate it. The Canadian mining code requires that we assume that the full magnitude of substation GPR is transferred out into mining areas if they are bonded together. In older mines where the distribution system is such that it is impossible to separate the substation ground from the mine ground system, and the economics of an isolation transformer are unreasonable, a method that might prove that GPR transfer levels are safe would eliminate a lot of heartache.
Thanks in advance for your thoughts on this.
In the case of the reports, the direct connection was over the ground wire on a overhead line out to a mining pit. I have a great deal of faith in the engineer running the tests and writing the reports but he is long since retired to ask questions of. My question is, has anyone ever seen a method for calculating the attenuation of GPR transfer over various types of ground connections?
I am not even certain I understand the mechanism by which it attenuates (capacitive charging current?) to begin coming up with a way to calculate it. The Canadian mining code requires that we assume that the full magnitude of substation GPR is transferred out into mining areas if they are bonded together. In older mines where the distribution system is such that it is impossible to separate the substation ground from the mine ground system, and the economics of an isolation transformer are unreasonable, a method that might prove that GPR transfer levels are safe would eliminate a lot of heartache.
Thanks in advance for your thoughts on this.
RE: Calculating Attenuation of GPR Transfer on OHL Grounds/Buried Grounds
For your "test" case, you had a buried pair of 250 MCM conductors between the generation and substation grids. Highly likely that a conductor of that size is not a solid, but a stranded construction - which means it is not a purely resistive element. That in turn means the observed impedance of the conductor can be affected by frequency - and obviously, by length.
Converting energy to motion for more than half a century
RE: Calculating Attenuation of GPR Transfer on OHL Grounds/Buried Grounds
If the connection between the two grids is by bare conductors, then you would need software that considers the voltage drop in the grid conductors. SES MALT considers all the ground conductors to be at the same potential. SES MALTZ calculates the voltage drop in the ground grid wires. MALZ calculates GPR at different points on the grid.
RE: Calculating Attenuation of GPR Transfer on OHL Grounds/Buried Grounds
Thanks, I will look at modelling options.
RE: Calculating Attenuation of GPR Transfer on OHL Grounds/Buried Grounds