Plywood Span Rating

Plywood Span Rating

Plywood Span Rating

(OP)
Hello Everyone.

I'm trying to understand what span rating is for a plywood but I don't get the right hand number. For example, if we have 24/0 or let's say, 32/16 I understand the left hand number means the span between joists across the long direction of the plywood but what is the right hand number? I read somewhere that it is the subfloor span or something but still it's not clear to me. I guess I don't much about subfloors. Can anyone explain with diagrams, if possible? Thank you very much in advance
Replies continue below

Recommended for you

RE: Plywood Span Rating

Hopeful answers your questions.

Link

RE: Plywood Span Rating

The first number is the recommended span length for roofs.
The second number is the recommended span length for floors.

RE: Plywood Span Rating

(OP)
So if it's 24/0 it means it's only for the roof? or is it for one story maybe? Thanks

RE: Plywood Span Rating

I've never used 24/0 but I think you are correct - no span rating for a floor.

RE: Plywood Span Rating

Only recognized for the roof, sounds right. I'm a bit flustered right now as my cats just got into a huge fight and I had to intervene.

RE: Plywood Span Rating

(OP)
also, some thicknesses are not found in the IBC table for some reason. That's something I wanna understand too. Thank you so much for your great answers!

RE: Plywood Span Rating

Also, I believe span ratings are for 2-span continuous minimum. So when the roofer replaces one bay of sheathing, he should be blocking underneath.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close