Better for what, specifically?
Ex "db" is flameproof construction (d) with level of protection "b" (high).
Basic design is strong enough to withstand internal explosion; flame path long enough to prevent ignition of external medium. Design allows internal ignition sources (like hot spots and sparks).
Ex "eb" is increased safety (e) with level of protection "b" (high).
Basic design is an increased safety level for normally non-sparking equipment. Design does NOT allow any unprotected sparking components inside.
In terms of enclosure construction and rating, the "db" criteria is generally more stringent, because it has to withstand an event created by the internal spark. The "db" design will tend to have better fits (component to component) and "custom" seals between moving and stationary parts in an effort to eliminate flame propagation from the internal volume to the surrounding external medium.
My guess - and it's only a guess, since I don't always deal with IEC ratings - is that the "db eb" rating means flameproof without having an internal spark capability. To me, that would seem to indicate that the "db eb" is likely a safer way to go.