(OP)
Dear Engineering Community,

I hope this message finds you well.

I am currently working on a project involving a 12kV distribution system, and I am looking for advice on effective methods to lower the fault current. This is a critical aspect of our system's reliability and safety, and any insights or recommendations from experienced engineers would be greatly appreciated.

Specifically, I am interested in:

  • Proven techniques or technologies that have been successful in similar applications
  • Any considerations or best practices to keep in mind during implementation
  • Potential challenges or pitfalls to be aware of
  • Recommendations for further reading or resources
Thank you in advance for your time and expertise. I look forward to your valuable suggestions.

Best regards,
Golden State EE
Replies continue below

Recommended for you

RE: Seeking Advice on Lowering Fault Current in a 12kV Distribution System

Higher source impedance, that's how you lower fault current.

Smaller transformers in substations, less intermeshing of the transmission network, no networking at the distribution level. Open ties rather than closed ties. Anything else you can do to increase source impedance.

But unless the fault currents are way outside the norms the attempts to reduce fault current levels could have multiple adverse impacts.

When one this sentence into the German to translate wanted, would one the fact exploit, that the word order and the punctuation already with the German conventions agree.

-- Douglas Hofstadter, Jan 1982

RE: Seeking Advice on Lowering Fault Current in a 12kV Distribution System

The solution on lowering fault current somewhat depends on what fault current you are trying to reduce. Three phase, phase to phase, or phase to ground.

RE: Seeking Advice on Lowering Fault Current in a 12kV Distribution System

Air core reactors.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Seeking Advice on Lowering Fault Current in a 12kV Distribution System

(OP)
@cranky108 We are trying to lower the three phase fault current at the secondary of the substation transformer so that when we perform "make before breaker" switching, the fault current wouldn't go over the equipment ratings.

RE: Seeking Advice on Lowering Fault Current in a 12kV Distribution System

That’s why you start out the transformer selection process by considering two of them in parallel.

I suppose that you could have a reactor between the buses that is in while both sources are paralleled and then bypassed when one of the sources is removed.

When one this sentence into the German to translate wanted, would one the fact exploit, that the word order and the punctuation already with the German conventions agree.

-- Douglas Hofstadter, Jan 1982

RE: Seeking Advice on Lowering Fault Current in a 12kV Distribution System

David that is where I would look also.

RE: Seeking Advice on Lowering Fault Current in a 12kV Distribution System

Over the years, on the construction side I have installed more than one reactor to limit fault currents.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close