I have a question about the 2015 IRC on joist spans.

Table R502.3.1(2) (residential living areas LL-40psf, DL-10psf, L/delta = 360) states that for a 2"x10" @ 16" SPF #2 the max span is 15'-5". But I have an engineered calc sheet (Woodworks Sizer 11 USA) that shows the max span is 15'. The calc sheet shows a clear span of 15'. When the IRC states 15'-5" span does it mean clear span?

Just curious why the IRC allows for a slightly longer span than engineering allows. I've added a copy of the calc sheet in case there was something missed in the calculation

Thanks all
Replies continue below

Recommended for you

RE: Floor Joists Code vs Engineering

Quote (2015 NDS 3.2.1 Span of Bending Members)

For simple, continuous and cantilevered bending members, the span shall be taken as the distance from face to face of supports, plus 1/2 the required bearing length at each end.

So that's 15' 3-1/2" clear for the IRC table. What kind of span do you get with no self weight? A very basic floor assembly usually has the joist included in the 10psf. Carpet, 1/2 plywood, joists, and 1/2 gyp ceiling. Doesn't add up to much. You might squeeze out an extra couple inches.

RE: Floor Joists Code vs Engineering

(OP)
That's exactly what it is. Soon as the self-weight was removed the max span worked out to be 15'-3 1/2".

I agree with you on what dead load should be. Usually spec a dead load of 15psf or higher depending on the floor finish.

Thanks for spotting the issue.

RE: Floor Joists Code vs Engineering

You may as well join the fun in the main forum under limits of prescriptive design...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close