I have a question about the 2015 IRC on joist spans.
Table R502.3.1(2) (residential living areas LL-40psf, DL-10psf, L/delta = 360) states that for a 2"x10" @ 16" SPF #2 the max span is 15'-5". But I have an engineered calc sheet (Woodworks Sizer 11 USA) that shows the max span is 15'. The calc sheet shows a clear span of 15'. When the IRC states 15'-5" span does it mean clear span?
Just curious why the IRC allows for a slightly longer span than engineering allows. I've added a copy of the calc sheet in case there was something missed in the calculation
Thanks all
Table R502.3.1(2) (residential living areas LL-40psf, DL-10psf, L/delta = 360) states that for a 2"x10" @ 16" SPF #2 the max span is 15'-5". But I have an engineered calc sheet (Woodworks Sizer 11 USA) that shows the max span is 15'. The calc sheet shows a clear span of 15'. When the IRC states 15'-5" span does it mean clear span?
Just curious why the IRC allows for a slightly longer span than engineering allows. I've added a copy of the calc sheet in case there was something missed in the calculation
Thanks all
RE: Floor Joists Code vs Engineering
So that's 15' 3-1/2" clear for the IRC table. What kind of span do you get with no self weight? A very basic floor assembly usually has the joist included in the 10psf. Carpet, 1/2 plywood, joists, and 1/2 gyp ceiling. Doesn't add up to much. You might squeeze out an extra couple inches.
RE: Floor Joists Code vs Engineering
I agree with you on what dead load should be. Usually spec a dead load of 15psf or higher depending on the floor finish.
Thanks for spotting the issue.