Intermittent fault in induction motor
Intermittent fault in induction motor
(OP)
I have one HV 3 phase star ungrounded induction motor. Sometimes there is a short duration of 5 milliseconds high magnitude currents recorded at its neutral side. The frequency of occurrence is random, sometimes even few days. How can a fault be of such type? Please suggest.
RE: Intermittent fault in induction motor
Do you mean that the 50/51N relay associated with the motor, is giving some current while the motor is running or at its start?
RE: Intermittent fault in induction motor
RE: Intermittent fault in induction motor
Could you please upload a copy of the SLD showing how 50/51N relay is connected specially showing how the NEUTRAL CT is connected?
RE: Intermittent fault in induction motor
RE: Intermittent fault in induction motor
Have you checked the wdg insulation for any possible faults?
Have you double checked the polarity connections of the CTs?
Is it a new motor commissioned recently or an old motor running without any trouble but giving this fault recently?
RE: Intermittent fault in induction motor
There may be a reoccuring external event causing the Y-B voltage to go high momentarily.
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Intermittent fault in induction motor
RE: Intermittent fault in induction motor
At this point I would consider a loose connection or a faulty relay.
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Intermittent fault in induction motor
But my concern is why 180deg out of phase.
Why don't you thinking replacing the CT set but it should be all six? Not that easy.
RE: Intermittent fault in induction motor
A spike in the incoming voltage may cause a current spike.
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Intermittent fault in induction motor
Also there are dual redundant relays mounted which recorded the same current nature.
RE: Intermittent fault in induction motor
Muthu
www.edison.co.in
RE: Intermittent fault in induction motor
But, the spikes being 180 degrees out, that indicates to me that the current is flowing out from Y and returning through B.
A high voltage transient may saturate the windings and cause spikes like that but it would also show on the line side CTs.
Is your supply system grounded and is the ground in good condition?
--------------------
Ohm's law
Not just a good idea;
It's the LAW!