Structural engineering for an MEP engineer...

Structural engineering for an MEP engineer...

Structural engineering for an MEP engineer...

(OP)
Hi all,

Hoping this falls within the forum allowable questions!

Bit of background: I'm an MEP & building physics engineer and my partner and I have bought a house.

Previous owners removed an internal wall (see attached SE drawing) but the builder has only installed support 1, but rather than the spec'd 203x203 they've installed a 152x152. There's no support 2 to be found.
They didn't (unsurprisingly) get BC signoff, but we are looking to get this regularised and of course be confident the house won't come down.

Here's my questions:

1) I know we'll need to go to an SE for a formal calculation but I'd quite like to be able to do it myself (or understand the results) - any good resources for this specific structural problem? I've a masters in physics so hopefully don't need too much background.
2) It'd be great if this were a simple problem that someone could tell me off the bat are we going to need to install new structure i.e. are we safe?
Replies continue below

Recommended for you

RE: Structural engineering for an MEP engineer...

It's not possible to give you the assurance you're looking for with the schematic you posted. It's not entirely clear what is being supported by these members or why you have CATNIC lintel for support 2. From a bit of googling seems like a pre-insulated steel member which suggests this is at the enclosure boundary but what loads are on it are unclear.

You need to:

a. Figure out where the load Support 2 was intended to pick up is going

b. Figure out the loads on all supports that are actually there

c. Analyze support 1 as simply supported and see if capacity exceeds your demand from (b) taking into account lateral torsional buckling. Not entirely sure of your British call-outs but a 152x152 UC23 ( ~ W150x18) has a max unbraced length of 1.5 meters. At 4.6 meters the moment capacity is ~ 45% of fully supported condition. Analyze any other member that is taking load in this arrangement (i.e. where load intended for support 2 went to)

d. Get a structural engineer to review this

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close