Floating roof Diesel Tank increase in water level- 200 tons- Reason and inspection recommendaion

Floating roof Diesel Tank increase in water level- 200 tons- Reason and inspection recommendaion

Floating roof Diesel Tank increase in water level- 200 tons- Reason and inspection recommendaion

(OP)
We have a floating roof tank which is used for storage of diesel. Following are the tank specification.

Diameter of Tank: 34 meter
Height of tank : 14 meters
Roof is double deck type
Make: Bernard & Smith
The roof of tank is double deck type and last refurbishment of tank was done in 2000 in which roof outer surface was cleaned and painted and inner surface was inspected.
Tank wall to floating roof seals were also replaced and currently no vapors leak is observed from tank wall to roof seal.

In recent rain event we have water level raised up inside the tank (measured and confirmed by DIP ) from 782 mm to 962 mm, which means around 200 tons of water went inside of tank. This was also confirmed as little water was found coming out of tank drain line. The roof water drain line also runs inside of tank to opening at bottom of tank.

We are planning to inspect the tank pontoons while in mean while can you guys help me in establishing following causes
1. From where the water went inside of tank either from Roof or drain line?
2. Whether there is chance of roof tilt or sink ?
3. What other precautions/inspection we have to perform?
Any feedback will help a lot

Replies continue below

Recommended for you

RE: Floating roof Diesel Tank increase in water level- 200 tons- Reason and inspection recommendaion

After 24 years, my guess is that your roof drain line is leaking / broken or blocked and hence entering the tank through roof vents or the external seals.

Roof tilt could happen, but unless there is a leak in the pontoons seems unlikely.

General inspection of seals, roof, floor, roof drain elbows and piping.

Find an experienced contractor....

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Floating roof Diesel Tank increase in water level- 200 tons- Reason and inspection recommendaion

[quote.... This was also confirmed as little water was found coming out of tank drain line. The roof water drain line also runs inside of tank to opening at bottom of tank.][/quote]

Apparently , there is no leakage of product thru the roof drain piping .
In this case im thinking two probability ;

- The roof inlet sump is leaking or ,

- The drain line is clogged and the rain water entered from emergency roof drains.


..

He is like a man building a house, who dug deep and laid the foundation on the rock. And when the flood arose, the stream beat vehemently against that house, and could not shake it, for it was founded on the rock..

Luke 6:48

RE: Floating roof Diesel Tank increase in water level- 200 tons- Reason and inspection recommendaion

(OP)
We have done some visual inspection from top platform of tank (as ladder steps degree is not suitable) to access on roof is not possible without any crane& man box.

From visual, we have found small holes due to corrosion on the top roof and seems water can seep from top roof. (In this case pontoons should also be leaking).

Regarding Drain line clogging and shear from any swivel joint, we have not witnessed any hydrocarbon coming out from roof drain and there is small quantity of water was found on roof.

Roof to tank wall seals seems to be the least likelihood as there is no HC vapors are coming out from space.

Rain water ingress from shear roof drain line is possible but in that case diesel should also come out which we have not witnessed.

My assumption is the leak from double deck roof but in this case, diesel should be present/found in pontoons.

My though process is following;

1. Inspection of pontoons and if HC/diesel found filled inside of pontoons then leak is from double deck roof.

2. If pontoons will be found empty, then leak will be Definity from drain line and in that case Darin line is sheared off and sitting on the tank floor (as drain line is 250 mm above from tank floor)

RE: Floating roof Diesel Tank increase in water level- 200 tons- Reason and inspection recommendaion

Depends where your pontoons are.

You seem to have a lot of water in your tank, Do you not drain it off?

It could be a mixture of things so don't leap to one conclusion.

If the tank hasn't been entered for 24 years there could be a significant amount of damage.

When there is no rain or water on the roof are you still getting water from the drain line?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Floating roof Diesel Tank increase in water level- 200 tons- Reason and inspection recommendaion

Why don't you suspect the diesel?

Check the upstream units that send diesel of any probable mal operation that has been concealed.

The log books could give you a clue.

DHURJATI SEN
Kolkata, India


RE: Floating roof Diesel Tank increase in water level- 200 tons- Reason and inspection recommendaion

(OP)
The DIP measurement only gives the outcome of increase in water level while the diesel level maintained the same.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close