Transformer Load Loses

Transformer Load Loses

Transformer Load Loses

(OP)
Can someone indicate how can I estimate my utility costs if I meter in the primary vs the secondary. Let assume a rate of 0.10 $/KW as a utility rate.
For the transformer I have this data:

Transformer data:

Vprim= 115kV
Vsec= 12.47kV
Rating (kVA) = 20000 55c/OA,26670 55c/FA,33330 55c/FA/FA
             = 22400 65c/FA, 29870 65c/FA, 37330 65c/FA/FA

Load Loss 99800 W
No-Load Loss 16823 W
Total Loss 116623
Perecnt Impedance = 9.19%



Replies continue below

Recommended for you

RE: Transformer Load Loses

joan271273
Do you need to make any correction to your post? Like the utility rate given is in $/kW instead of $/kWH?
calculating the metering on the primary side seems to be unchanged, though there are possibilities of calculating the auxilliary supply cost inclusive.
However if you want to make cost calculation based on the metering on the secondary side, then the capitalised cost of all the load and noload losses need to be incorporated.
Some further data are also required like load pattern or the number of hours of loads, interest rate. All these need to be capitalised for the life of the transformer. Generally you must have the capitalised cost of load and noload losses at the time of procurement of the transformer. Those values can be utilised to determine the charges for the transformer losses. the calculation can be very simple, in which case the probability of being correct is lower compared to the complex calculation. You will have enough information in GE Distribution Data book.
Regarding the data of losses which you have given please indicate the load loss data is on the basis of the OA or FA or FA/FA rating. I have found this always confusing.

RE: Transformer Load Loses

I might suggest REA Bulletin 65-2 April 1978 Evaluation of large power transformer losses.  This guide steps you through the process in determining cost of ownership of the transformer due to losses.  You will have to refer to the transformer test data but typically losses are expresed in terms of the base OA of the unit.

RE: Transformer Load Loses

joan271273
Joan you need to create a loss curve for this transformer.If you meter on the primary the losses will be included in the utility bill-secondary metering will not include these losses. The information you have provided for this transformer is sufficient to create this curve. I have been out of the country for two months and do not have the time  today to calculate this curve. In any event I will provide something by next Thursday.
Jack6238

RE: Transformer Load Loses

(OP)
Thanks for the offer to develop this curve, do you think the REA document listed in a previous thread a good source for this. I am still trying to locate a copy.

Thanks

RE: Transformer Load Loses

Suggestions:
1. Cooling clarifications are needed, e.g. FA/FA (What about FOA?)
2. Clarify the cooling type for normal continuous operation
3. Losses will increase with the increased cooling, e.g. for FOA
4. Transformer worst case manufacturing tolerances
5. Check ANSI/IEEE C57.12.00-1987 or latest and related references for more info.
6. Etc.

RE: Transformer Load Loses

joan271273
I will create the curve in an excel spread sheet and either fax or email the file. In the meantime, this transformer has an X/R ratio of 18.3897, a peak efficiency occurring at 41.06 % load on a 20 MVA base,the % iron loss is .084115 and the % copper loss is .499. I will use this data to construct the efficiency curve vs per unit load. From this curve you can determine the losses at any value of load and calculate the operating cost for secondary metering. Please send fax number or email information.
This topic is covered in detail in several transformer books. the one I like the best is
The J&P Transformer Book-11th Edition, A Practical Technology of the Power Transformer, by Franklin and Franklin.

RE: Transformer Load Loses

joan271273
I have finished the curves. I have created an efficiency curve and a loss curve. I await your fax or email and I will send. I have created curves for a load power factor of .8 and 1.0. If you will send the operating power factor, I will create a unique curve for the exact operating condition. The unit has an efficiency of 99.4986 % at ~40 % load at a power factor of .8 and an efficiency of 99.5985 % when operated at ~40 % load at a power  factor of 1.0. The unit operates above 99 % efficiency at nearly all values of load.

RE: Transformer Load Loses

(OP)
Jack6238, I do not have your fax# or e-mail. I the following Fax # 408 920 9768

Thanks for your help

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close