Line Differential Protection Susceptance Calculations - Please help!!

Line Differential Protection Susceptance Calculations - Please help!!

Line Differential Protection Susceptance Calculations - Please help!!

(OP)
Good day protection engineers,

I am struggling to see how in the SEL 411L protection manual example they managed to convert the line primary susceptance values to secondary values. I understand the primary values are derived from line characteristics like impedance, capacitance, geometry etc and short circuit program can determine it.

We have the following :

Line length : 70 miles
CT ratio (at this end) : 1600:5A
VT Ratio: 500kV:111.11V
Line voltage : 500kV
Positive sequence susceptance : 0.009 mS/mile (primary).

So the total susceptance will be : 0.009 mS x 70 = 0.000 63 S.

When reflected to secondary, they obtained 8.86 mS. Can someone explain how they got this value please. I tried multiplying the primary value by the CT Ratio/VT ratio but seems wrong. Is there anything I am missing?

RE: Line Differential Protection Susceptance Calculations - Please help!!

You seem to be using the right formula, if you are using Ohms, but you are using Smho, so what should the formula be?

RE: Line Differential Protection Susceptance Calculations - Please help!!

@Ashsdgee,
I got 12.75 milliSiemens. IDK if that's worthwhile.
The formula when referring to the secondary needs the voltage and the VA bases.
Ynew=Yold X (kVold/kVnew)^2 X (kVAnew/kVAold)
Perhaps the conductance portion was left out causing the error. Susceptance is just the imaginary part of the admittance

RE: Line Differential Protection Susceptance Calculations - Please help!!

I get their answer by multiplying .00063*PTR/CTR. That seems right to me - the equation for secondary susceptance should be the inverse of the normal secondary impedance calculation.

Casey

RE: Line Differential Protection Susceptance Calculations - Please help!!

My bad. I missed the title of the topic. Yes, the formula for calculating the susceptance from primary siemens to secondary is just multiplying the value to the PTR divided by the CTR. It is because the admittance of lines is assumed to be purely susceptance, so no conductance!

RE: Line Differential Protection Susceptance Calculations - Please help!!

(OP)
Many thanks for your replies . Yes @Parchie I had swapped the CTR/VTR around as mentioned.

RE: Line Differential Protection Susceptance Calculations - Please help!!

@Ashdgee,
I understand SEL 411L needs to have the susceptance values so it can compensate for the charging current in the differential protection logic. IIRC, if one uses the positive susceptance alone, the accuracy of the protection is going to be a bit inaccurate. SEL has a paper on that. I have searched the web and found it HERE.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close