HAC Hazardous Area classification

HAC Hazardous Area classification

(OP)
Folks;
did we consider in stds like API 505, IP 15 that flange connections are within class 0, 1 or 2?
Replies continue below

Recommended for you

RE: HAC Hazardous Area classification

Quote (wd1980)

did we consider in stds like API 505, IP 15 that flange connections are within class 0, 1 or 2?
Negative as flanges relate to grade of release and are not relevant to zoning (0/1/2) directly.

Quote (EI 15-2015)

1.5.4 Source and grade of release
For the purpose of area classification a source of release is defined as a point from which a flammable gas, vapour or liquid may be released into the atmosphere. Three grades of release are defined in terms of their likely frequency and duration:
−− Continuous grade release: A release that is continuous or nearly so, or that occurs frequently and for short periods.
−− Primary grade release: A release that is likely to occur periodically or occasionally in normal operation i.e. a release which, in operating procedures, is anticipated to occur.
−− Secondary grade release: A release that is unlikely to occur in normal operation and, in any event, will do so only infrequently and for short periods, for example as might result from operator error or foreseeable equipment failure, such as a leak resulting from failure of flange gasket, or seal on a pump or valve etc.
The grade of release is dependent solely on the frequency and duration of the release. It is completely independent of the rate and quantity of the release, the degree of ventilation, or the characteristics of the fluid, although these factors determine the extent of vapour travel and, in consequence, the dimensional limits of the hazardous area.

You should start with studying standards you have mentioned.

RE: HAC Hazardous Area classification

(OP)
Dear Sir;
thanks for the reply!

May I was not clear enough in the post, I know the sdt, I should wrote if we have a leak in a flange ( which is not a normal operation ) what ever the leak rate or duration then
should the surrounding area be considered in HAC or since it is not a normal operation then I have not to consider this.

RE: HAC Hazardous Area classification

Quote (wd1980)

should the surrounding area be considered in HAC or since it is not a normal operation then I have not to consider this.
Positive, you should consider HAC

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close