Zone 22 equipment

Zone 22 equipment

Zone 22 equipment

(OP)
Question in zone 22 (dust) is it allowed to install non-certified equipment, however it meets the requirements of industrial equipment such as IP 6x, surface temperature, non-sparking (junction box, switch, luminaires)If possible, what standard does it indicate?

RE: Zone 22 equipment

The NEC, NFPA 70, requires the equipment installed in a Zone 22 location to be listed and marked as suitable for the location. This is a bit more restrictive than the NEC requires for a Class II, Division 2 location.

CODE

506.20(C) Zone 22.  In Zone 22 locations, only equipment listed and marked as suitable for the location shall be permitted. 

Exception No. 1:  Apparatus listed for use in Class II, Division 1 or Class II, Division 2 locations with a suitable temperature class shall be permitted. 

Exception No. 2:  Pressurized equipment identified for Class II, Division 1 or Division 2 shall be permitted. 

Exception No. 3:  For Group IIIA materials, equipment listed for use in Class III, Division 1 or Class III, Division 2 locations with a suitable temperature in accordance with 500.8(D)(3) shall be permitted.] 

RE: Zone 22 equipment

(OP)
Tanks for feedback!!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close