I am trying to find solutions for a lab space with fume hoods of a total of 5000m3/h exhaust rate. The makeup air cannot come from adjacent spaces, it has to be outdoor air. Also the makeup air should not be supplied directly into the hoods. The diversity factor will range from 25% to 100%.
The space has to be maintained at 23oC and 50%RH. I calculate the sensible heat gain from walls, windows and equipment to be around 18kW. Space latent cooling loads are negligible. The ventilation cooling loads are 22kW sensible + 29 kW latent.
One of the solutions I am evaluating is the installation of an AHU which will be supplying preconditioned, cooled and dehumidified, makeup air. The air has to be cooled to the space's dew point to completely remove the ventilation latent load. At this temperature the volume rate of the air can also remove the space heat gain, thus an indoor unit (VRF, split, fan coil) is not needed.
For the times when not all hoods are in use, air will have to return to the AHU and mix with the fresh makeup air such that the fresh air intake rate matches the exhaust rate from the hoods. Exhaust from the AHU is not needed.
My question is how can this be implemented? How can the intake be controlled to match the exhaust? Can the AHU be of a single fan (supply fan, without return or relief fan) circulating 5000m3/h, with modulating return and fresh air dampers to control the mixing ratio and thus intake rate?
(ciqa.net)
The dampers could be modulated by a PI/PID controller to maintain a set differential pressure between the room and the environment (either zero or slightly negative ≈-15Pa). Will this work? Are there problems in this idea?
The space has to be maintained at 23oC and 50%RH. I calculate the sensible heat gain from walls, windows and equipment to be around 18kW. Space latent cooling loads are negligible. The ventilation cooling loads are 22kW sensible + 29 kW latent.
One of the solutions I am evaluating is the installation of an AHU which will be supplying preconditioned, cooled and dehumidified, makeup air. The air has to be cooled to the space's dew point to completely remove the ventilation latent load. At this temperature the volume rate of the air can also remove the space heat gain, thus an indoor unit (VRF, split, fan coil) is not needed.
For the times when not all hoods are in use, air will have to return to the AHU and mix with the fresh makeup air such that the fresh air intake rate matches the exhaust rate from the hoods. Exhaust from the AHU is not needed.
My question is how can this be implemented? How can the intake be controlled to match the exhaust? Can the AHU be of a single fan (supply fan, without return or relief fan) circulating 5000m3/h, with modulating return and fresh air dampers to control the mixing ratio and thus intake rate?
(ciqa.net)
The dampers could be modulated by a PI/PID controller to maintain a set differential pressure between the room and the environment (either zero or slightly negative ≈-15Pa). Will this work? Are there problems in this idea?
RE: AHU design for space with high exhaust air requirements
You can recover heat from the exhaust with a runaround loop to the make-up air. (Cross-contamination between the air streams must be avoided).