Failing chilled water pipe insulation
Failing chilled water pipe insulation
(OP)
I work on a University campus that has been experiencing degradation\failure of chilled water pipe insulation. The installations are all 10 to 20 years old utilizing Armaflex closed cell elastomeric foam, the failure is always on the supply pipe (chilled water supply temp is approx. 42°F, return is 48 to 50°F). The insulation begins to wrinkle, pucker, and collapse in on itself resulting loss of thickness and R-value eventually leading to sweating pipes. This is occurring in numerous buildings of all different types (Labs, Offices, Dorms). Has anybody seen anything like this or have an idea what is causing it?
RE: Failing chilled water pipe insulation
Has this damage occurred just recently, or has it been deteriorating throughout the entire life of the system?
RE: Failing chilled water pipe insulation
RE: Failing chilled water pipe insulation
This document from Armaflex shows similar symptoms, although it's not very informative: https://www.armacell.us/fileadmin/user_upload/Whit...
This explains how Armaflex is great, and the best insulation to use to prevent CUI - yet.....
https://local.armacell.com/fileadmin/cms/downloads...
RE: Failing chilled water pipe insulation
RE: Failing chilled water pipe insulation
RE: Failing chilled water pipe insulation
Is that line where the installation gap was if this is "split" post install insulation?
Very interesting that there is only 5C difference between the two lines.
Is there ANY possibility that the supply line could have gone to or below freezing at any point. Hence any water or moisture could freeze inside the insulation? Might only be for a few hours, but once those bubbles break, they don't repair themselves?
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Failing chilled water pipe insulation
- Armaflex
- Foam Glass
- Fiberglass
- Cork
Today I consider a CUI coating vital to long term performance of cold piping, unless the piping material is inherently non corrosive. In the past 20 years CUI coatings have improved to the point where their is no question as to the benefit of CUI coatings.Even with CUI coatings, ongoing maintenance of insulation systems - particularly components that keep the system dry is important and often neglected.
RE: Failing chilled water pipe insulation
RE: Failing chilled water pipe insulation
Most of the information needed for design can be found at the Plastic Pipe Institute https://www.plasticpipe.org/MunicipalIndustrial/Mu...
RE: Failing chilled water pipe insulation
I would suspect an insufficient insulation thickness is allowing water to condense within the void between the insulation and the piping, and eventually "leaking" out at insulation seams; my guess is that is why you see the water stains in your last pic.
Once it is wet inside, the only way to dry it is to shut the plant down and pull off the old waterlogged insulation.
Once the pipe is dry, if you glue-on the first layer, it will help eliminate the voids.
You may also need more than one layer.
RE: Failing chilled water pipe insulation