Generator is not starting - Volvo Penta Engine

Generator is not starting - Volvo Penta Engine

Generator is not starting - Volvo Penta Engine

(OP)
Hi!

I was requested to troubleshooting a genset composed of Comap InteliGen-NT controler and Volvo Penta TWD1644GE engine which is not startig, either in auto or manual mode. When I gave a command to start the dysplay just blink followed by "WRN ECU" alarm.
All CAN connections and controller parameters have been checked with no abnormalities.
Have you guys experienced similar issue?
Replies continue below

Recommended for you

RE: Generator is not starting - Volvo Penta Engine

Probably you will need to be more specific. The engine is not turning over at all, or it isn't starting? Sounds like it isn't turning over or attempting to start at all?

RE: Generator is not starting - Volvo Penta Engine

Has the ECU been replaced?
Has anything been replaced recently?

--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Generator is not starting - Volvo Penta Engine

Is it even getting a start signal?

When one this sentence into the German to translate wanted, would one the fact exploit, that the word order and the punctuation already with the German conventions agree.

-- Douglas Hofstadter, Jan 1982

RE: Generator is not starting - Volvo Penta Engine

This alarm occurs when an ECU is configured, but the communication with the ECU is not established or has dropped out - https://www.manualslib.com/manual/1602539/Comap-In...

Suggest regardless of connections checked and parameters verified, things aren't chatting with each other.

RE: Generator is not starting - Volvo Penta Engine

Quote:

When one this sentence into the German to translate wanted, would one the fact exploit, that the word order and the punctuation already with the German conventions agree.
This may give some insight into some German schematics that I have encountered, without actually imparting understanding.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Generator is not starting - Volvo Penta Engine

Your battery is dead.

Put your multimeter on it. While the the starter is engaged you'll likely see the battery voltage drop below 9 volts for a 12v system or 18v for a 24 system.

It's frustrating that nobody considers the box full of acid to be the most likely component to have problems in an engine starting system.

RE: Generator is not starting - Volvo Penta Engine

Possibly . . .

However, despite dpc's request, OP has not yet stated precisely what's or what's not happening during starting attempts, viz., is engine not cranking at all?

Is solenoid even engaging starter?

Is it that cranking is sluggish?

Or is cranking healthy but engine just not firing at all?

Or is engine sputtering and firing a bit, but just not catching?

Saying what the error code is, if any, is helpful, but doesn't tell the complete story; it's difficult for anyone to assist you with diagnosing something if only partial or incomplete details are provided.

As has been stated here repeatedly, more information yields better answers.

Your turn, Thiago.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

RE: Generator is not starting - Volvo Penta Engine

OP has said everything that needed to be said. The display blinking indicates it is losing power. The "WRN ECU" alarm indicates the can nus link is being interrupted due to loss of power.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close