I have not been able to find any information on shearwall collectors on the Canadian wood code - CSA086. I see people on the forum talking about it but I found strange that the Canadian code seems to make no provision for it. Am I missing something? Is it a shear wall requirement? Where can I find good literature on it?
RE: Shear Wall Collectors - CSA 086
RE: Shear Wall Collectors - CSA 086
RE: Shear Wall Collectors - CSA 086
So when I've got a greener engineer on a project at my office, I always try to get them to start on the lateral. Because honestly, I can get gravity designs to work out 99% of the time as long as I've already got the lateral worked out. Nothing worse than going back to the client late in the game saying you need more shearwalls, or more bracing, or thicker floor sheathing for the diaphragm loading. But changing a beam size late in the game, as long as it's not drastic, no one cares.
RE: Shear Wall Collectors - CSA 086
It took me about a year to realize exactly what you said, lateral systems are going to be my big challenge. Most of my posts on this forum concern lateral systems. And I especially agree with what you said about going back to the client.
Cheers!
RE: Shear Wall Collectors - CSA 086
RE: Shear Wall Collectors - CSA 086
RE: Shear Wall Collectors - CSA 086
RE: Shear Wall Collectors - CSA 086
RE: Shear Wall Collectors - CSA 086
To be fair, I don't practice in seismic, so keep that in mind.
RE: Shear Wall Collectors - CSA 086
Your method of just checking the unit shear at the interface of the wall is, from my experience, common industry practice but in my opinion not in accordance with the continuous load path requirements of the building code. Collectors/drag struts are required for all partial depth lateral resisting elements. Terry Malone’s book covers this and this is a past post that also has some good info: Link
RE: Shear Wall Collectors - CSA 086
In most wood structures, we're fortunate in that the collector and the chord are generally the same thing AND are generally braced in both axes every 16 to 24 inches, making their compressive capacity grossly higher than what is needed in all but the most massive and open of wood structures.
So as long as your diaphragm has a chord (which it has to, or it isn't a diaphragm), you probably have a collector - even if only by mistake.
RE: Shear Wall Collectors - CSA 086