Multiple Holes in Floor Joist
Multiple Holes in Floor Joist
(OP)
I was asked to analyze a series of floor joists that have multiple holes. The code does not address how many holes can be installed next to each other. In this case I think a minimum spacing of 4inches is required to prevent splitting. I am trying to find a reference regarding this concern. Thank you for your help
This is what I got from the client.
1. Joists are DF#2
2. Hole diameter 1-1/2"
3. Distance between two consecutive hole is 2"
4. Joists are 2x10
This is what I got from the client.
1. Joists are DF#2
2. Hole diameter 1-1/2"
3. Distance between two consecutive hole is 2"
4. Joists are 2x10
RE: Multiple Holes in Floor Joist
RE: Multiple Holes in Floor Joist
The shear stresses could be an issue close to the supports. But, in my view, the biggest issue is worrying about splitting (which will affect both bending and shear).
Conceptually, I look at this similarly to web openings in wide flange beams (because I'm more of a steel guy) where the preferred reinforcement method would be some sort of horizontal reinforcement above and below the penetrations. Maybe just running a couple of steel straps along that length of the beam where those penetrations are. But, the question is how to do this without risking more splitting..... I think it can be done, but I don't know what precautions should be taken to prevent it. Maybe using higher gauge nails for the straps?
RE: Multiple Holes in Floor Joist
NZ Wood Design Guides: Reinforcement of Timber Members
If you determine that this is a problem (probably is), best bet is likely to remove the conduits, install plywood on both sides (glue it on and then screw/nail it). Do one side at a time, drilling the plywood each time at the existing holes to prevent additional damage.
RE: Multiple Holes in Floor Joist
RE: Multiple Holes in Floor Joist
You may find the NJ code is based on the National building code and has holey joist rules that look a lot like the section of the Massachusetts Code in the pdf presentation in the above link.
All those holes in a row, with a bunch of splitting and blown out material of unknown depth is a little disquieting, at least to me.
RE: Multiple Holes in Floor Joist
I dug into this a while back. From what I can tell, those guidelines are 100% empirical. I found identical notching and boring guidance in publications back to the early 20s with no evidence of engineering analysis or testing. Just a 'this is what we do, and it works.' Unfortunately, that depends on people not drilling 10 holes in a row. After all, houses in the 20s didn't have 30 electrical circuits, a web of Pex piping, hard wired internet infrastructure, AV cabling, etc. all running over top of the living room.
There's plenty of literature out there for reinforcing Engineered wood products - the manufactures have a vested interest in making sure their product isn't the reason for a headache. But commodity lumber? There isn't really a push for that, especially as its use for floor framing falls further and further out of use. So there's not much out there for a good, US code compliant fix.
RE: Multiple Holes in Floor Joist
I don't like how it appears the electrician damaged the joists during drilling. I could be wrong here but it kinda looks like a layer of wood busted off. It looks like maybe the back side of the hole spalled off by the pressure of the drill tip like a bullet exit wound. I also don't like how closely spaced holes are. Shear failure will look like splitting and the failure plane will probably travel through all the holes.
That being said, you still might be able to justify this without retrofit. What are your moment and shear ratios at worst case hole locations without considering cores? My guess is the electrician might have taken away 50% of your shear capacity and at most 10% of your moment capacity, just a ballpark estimate. If I really wanted to dig into this I guess I would model the joist as shell elements to get a better handle on stress concentrations around the holes.
RE: Multiple Holes in Floor Joist
-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates
-Dik
RE: Multiple Holes in Floor Joist