Kindly through some light on how to calculate the breaking current capacity of a MCCB?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting Guidelines |
Kindly through some light on how to
|
Kindly through some light on how toKindly through some light on how to(OP)
Kindly through some light on how to calculate the breaking current capacity of a MCCB?
Recommended for youRed Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! Already a Member? Login |
News |
Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.
Here's Why Members Love Eng-Tips Forums:
Register now while it's still free!
Already a member? Close this window and log in.
RE: Kindly through some light on how to
I’ll see your silver lining and raise you two black clouds. - Protection Operations
RE: Kindly through some light on how to
BC = 1.732 * V * A * 10E-6
BC is breaking capacity in MVA
V is the rated service voltage in volts
A is the short circuit current in amperes
Converting energy to motion for more than half a century
RE: Kindly through some light on how to
" Kindly through some light on how to calculate the breaking current capacity of a MCCB?"
The learned advice by Mr. davidbeach is short and sharp. A great post.
I would like to add the following for clarity, for your information.
1. In the IEC world, a) rated ultimate short-circuit breaking capacity (Icu,..is the maximum short-circuit current value which the CB can break twice (O-t-CO) at the corresponding rated operational voltage. After the opening and closing sequence, the CB is [b]NOT required to carry the rated current.
b) Rated service short-circuit breaking capacity (Ics), ..._is the maximum short-circuit current value which the CB can break three times in accordance with a sequence of opening and closing operation (O-t-CO-t-CO) at a defined voltage of (Ie) and at a defined power factor. After the sequence, the CB is required to carry its rated current.
2. Note: a) Testing procedure and judgment differ between IEC (in Europe) and IEEE/NEMA (in US). The same CB rated X kA per IEC is very likely to be rated Y kA per IEEE/NEMA.
b) This result to test certification or EC mark in Europe is NOT automatically as being listed/recognized by UL in the US.
3. IEC in (Europe) and IEEE/NEMA (in US), each publishes/issues their own "standard" without any co-ordination or harmonisation.
4. The IEC and IEEE/NEMA do NOT carryout any testing or policing that their "standard" is correctly implemented/interpreted.
Che Kuan Yau (Singapore)