Kindly through some light on how to calculate the breaking current capacity of a MCCB?
Replies continue below

Recommended for you

RE: Kindly through some light on how to

2
You don't calculate it, you read it off the nameplate. The relevant IEEE or IEC standard may then provide guidance for adjusting that rating (downward) when the prospective fault current X/R exceeds the test value.

I’ll see your silver lining and raise you two black clouds. - Protection Operations

RE: Kindly through some light on how to

Breaking capacity formula (does not matter what type of breaker is used).
BC = 1.732 * V * A * 10E-6

BC is breaking capacity in MVA
V is the rated service voltage in volts
A is the short circuit current in amperes

Converting energy to motion for more than half a century

RE: Kindly through some light on how to

Mehak kar (Mechanical)(OP)2 Dec 23 18:55
" Kindly through some light on how to calculate the breaking current capacity of a MCCB?"
The learned advice by Mr. davidbeach is short and sharp. A great post.
I would like to add the following for clarity, for your information.
1. In the IEC world, a) rated ultimate short-circuit breaking capacity (Icu,..is the maximum short-circuit current value which the CB can break twice (O-t-CO) at the corresponding rated operational voltage. After the opening and closing sequence, the CB is [b]NOT required to carry the rated current.
b) Rated service short-circuit breaking capacity (Ics), ..._is the maximum short-circuit current value which the CB can break three times in accordance with a sequence of opening and closing operation (O-t-CO-t-CO) at a defined voltage of (Ie) and at a defined power factor. After the sequence, the CB is required to carry its rated current.
2. Note: a) Testing procedure and judgment differ between IEC (in Europe) and IEEE/NEMA (in US). The same CB rated X kA per IEC is very likely to be rated Y kA per IEEE/NEMA.
b) This result to test certification or EC mark in Europe is NOT automatically as being listed/recognized by UL in the US.
3. IEC in (Europe) and IEEE/NEMA (in US), each publishes/issues their own "standard" without any co-ordination or harmonisation.
4. The IEC and IEEE/NEMA do NOT carryout any testing or policing that their "standard" is correctly implemented/interpreted.
Che Kuan Yau (Singapore)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close