Typically, a Stabilizing Resistor is incorporated into a High Impedance Type REF Protection Scheme to reduce the sensitivity of the relay and prevent it from triggering during through fault conditions, particularly if there is saturation in one of the Current Transformer (CT). The resistor is carefully calculated to ensure that under external fault conditions (at max fault level), the voltage generated by an unsaturated CT does not cause a current flow exceeding the relay's preset threshold. This setup aims to avoid unnecessary relay operation during external faults.
However, a concern arises regarding whether the relay might remain desensitized even during internal faults (In Zone faults), where the fault current magnitude is generally lower than that of a full external fault. The question arises because, by introducing the stabilizing resistor, the relay has already been desensitized against responding to a full fault current. In this scenario, how does the relay still receive sufficient current during an internal fault?