Hi!

I am currently reviewing a proposal involving the use of A-36 "unheaded" stud anchors welded to a steel pile plug for concrete shear transfer, where tension is not anticipated.

As per my examination of AISC360-16, specifically in the I.8 Steel Anchors chapter, the documentation primarily addresses calculations for headed studs. The scope of AISC360-16 seems to be limited to headed anchors, and I am encountering a gap in guidance regarding the application of unheaded bolts in this context.

While the conceptual use of unheaded bolts appears reasonable for the intended purpose, I am seeking clarification on whether AISC360-16 provides any specific guidance for such scenarios.

I would greatly appreciate any insights or recommendations you may have on how to proceed.
Replies continue below

Recommended for you

RE: Steel "Unheaded" Stud Anchors in Composite Components

How long, and are they deformed?

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik

RE: Steel "Unheaded" Stud Anchors in Composite Components

Is this meant to be a shear friction application? If so, then this will fall under ACI 318.

You say there is no tension, do you mean that there is no tension from the external force or no tension in bending?

Under your typical bending application (shear transfer), headed studs help to make sure the concrete to stud bond isn't the controlling factor and the concrete is held in place by the headed studs.

RE: Steel "Unheaded" Stud Anchors in Composite Components

That's what I was thinking...

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik

RE: Steel "Unheaded" Stud Anchors in Composite Components

Look at the AISC Specification Chapter I first paragraph. It doesn't cover this situation. I'd start searching scholar.google.com for this question. LOL

RE: Steel "Unheaded" Stud Anchors in Composite Components

(OP)
Thank you all for the replies. @WesternJeb, if this falls under ACI 318, then what is your opinion on what chapter should apply? The same as for those shear lugs in base plates? Chapter 17.11 of ACI 318-19?

RE: Steel "Unheaded" Stud Anchors in Composite Components

(OP)
Short update: maybe I was missing the concepts regarding the types of anchor studs, which can be whether headed or headless studs according to AWS D1.1.

It seems like DBA's (deformed bar anchor) complying with AWS D1.1 are headless studs type C cold worked low carbon steel fabricated under ASTM A496.

Just found this in this nice 2015 article Link

No information, however, regarding ASTM A36 carbon steel "fabricated" rods which are used as studs. I'm still stuck here.

RE: Steel "Unheaded" Stud Anchors in Composite Components

TTomaz, it depends on your application. I understand you have a steel pile plug, but which part? What forces are you intending to resist?

If it is a pure shear force being applied, then your strength would be based on basic material properties of your steel shear strength, weld strength, concrete breakout, etc.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close