Isolated phase service entrance conductors

Isolated phase service entrance conductors

Isolated phase service entrance conductors

(OP)
We had a project where the utility required isolated phase construction for a 2500a, 480V service.

What they wanted was that the parallel 7 sets of conductors had to be run separated by each phase to the service disconnect.

I never heard of this, and had to research the NEC to verify that was even legal.

The utility rep really did not have a good answer when I questioned the purpose. (they stated this way all three phases may not be lost if one leg faults and melts the conductor).

Does anyone know why this would bw an advantage to the utility?

RE: Isolated phase service entrance conductors

See: A) Article 300-20 induced currents in metal enclosure or raceways.
     B) Article 310-4 parallel conductors.

Easier to terminate, cables do  not cross each other.
 
If underground is it in PVC?
How is the system grounded?
How do you penatrate metal service equipment?

RE: Isolated phase service entrance conductors

(OP)
yes, the requirement was to run PVC underground. there ia an artical in the nec for isolated phase conductors. penetrating the service gear enclosure required cutting sots between the conduit hole cutouts in the enclosure, or removing a square section if I remember correctly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close