Exhausting heat from electrical room - check my calcs?
nuuvox000
344
I'm trying to figure out how much exhaust CFM I would need to provide to cool an electrical room with transfer air from surrounding spaces. It has a 115 kVA transformer inside; it looks like these are typically about 95% efficient so 5% would be given off as heat in the room. So I'm looking at about 5.75 kW, which is about 19,600 BTU/hr. I'd like it to turn on at 90 °F and turn off at 85 °F. Air would be coming from the corridors at approximately 75 °F.
My equation for sensible gain is CFM*1.1*▲T*AF
CFM = cubic feet per minute
1.1 = constant in BTUh/CFM-°F
▲T = temperature difference
AF = altitude factor (0.85836 at my altitude)
So CFM = q_s/(AF*1.1*▲T)
19600/(0.85836*1.1*(90-75)) = 1385 CFM
Am I right in using this equation? Thanks in advance.
You wouldn't get down to 85F though.
I calculated about 1800 CFM.
That's a lot of air....
Thanks for the response, I'd love to know how you calculated that if you have time. Yes, and there are three of these rooms so it's 3 times a lot of air. My plan is to recommend mini splits for these spaces but I just wanted to make sure I had calcs to back it up too.
The equation you are using is correct. I don't know about the altitude correction factor but the basic equation is correct.
I have a spreadsheet attached from the previous company I worked for that estimates heat loads from electrical equipment. Attached is spreadsheet for transformers. For 112.5 kVA transformer heat load is 11,604.2 btu/hr.
Based on this and the equation assuming the correct altitude correction factor I calculate the air flow required = 820 CFM for 90 F resulting temperature.
The actual maximum design temperature for electrical equipment is 104 F, based on this the actual air flow required = 420 CFM approx.
Thanks, Snickster! I think you're right that I could take up the temperature in the room. It's still a lot of air and we're going to be doing a heat recovery VRF system anyway, so I'm going to push them to fan coils unless they really push back and want exhaust.