Let’s not “bury the lead” here folks. 0.18kW is 1/4 HP, this is a very small blower motor, most likely Shaded Pole or at best, PSC type. In 99% of single phase motors that small, they are going to be made as “Thermally Protected”, meaning the motor itself has a built-in thermal protective device to protect against overload. It should say so right in the nameplate of the motor, or at the very least in the manufactures data sheets. Sometimes it is a simple thermal switch in the motor housing, sometimes in the case of Shaded Pole type motors it is the form of the motor itself being designed to be able to withstand locked rotor current indefinitely (called “Impedance Protected”).
In either case, you only need Feeder protection sized for the conductors going to it. Before adding superfluous devices to the circuit, I suggest that you investigate that motor a little more.
If you DO determine that it needs external protection, a Motor Protection Circuit Breaker is always sized to the motor nameplate Full Load Amps. Starting current is factored into the trip curve of the thermal protection in that breaker.