Recently, we got a requirement for 15 meters (50 feet) safety distance for the fired heater. Despite not being able to find this "number" in any standard (please correct me), I want to understand if my interpretation is correct.
The primary reason for the minimum clearance of 15 meters is to prevent ignition of gases/liquid incoming from adjacent equipment that could leak. Is this correct?
The primary reason for the minimum clearance of 15 meters is to prevent ignition of gases/liquid incoming from adjacent equipment that could leak. Is this correct?
RE: Fired heater safety distance
RE: Fired heater safety distance
RE: Fired heater safety distance
RE: Fired heater safety distance
One is not prohibited to designate an uncontrolled source of ignition (open flame and overheated surfaces in your case) close to a process side if release sources are controlled or segregated (e.g. steam curtain).
Your question concerns zoning (fire, ex) - note that any option is possible if it has been justified properly. Resulted risk is the only issue.
RE: Fired heater safety distance
My problem is actually a request from one vendor to have a safety distance of 15 m for the Electrical Heater. Since the electrical heater is contactless i.e, process fluid is in a tube/pipeline surrounded by a heating element, then all is surrounded with insulation closed in the box, which is under slight N2 pressure.
There is no chance that gasses from external leaks (surrounding equipment), reach heating elements and generate explosions.