Mothballing - Air gap vs Blanking

Mothballing - Air gap vs Blanking

Mothballing - Air gap vs Blanking

(OP)
We are currently working on mothballing a PSM covered plant. When I've done mothballing at past companies, I've always been taught to air gap the equipment in order to call it mothballed in PSM but there is a question if we have to air gap it or if slip/pancake blanks would be adequate. I don't believe there is a regulation on this, but was curious about what is considered the industry standard.
Replies continue below

Recommended for you

RE: Mothballing - Air gap vs Blanking

" mothballing" is not a defined term anywhere I know, but is simply a step towards abandonment, but without the costs or legal issues associated with abandoning something. So everyone is their own standard.

What's PSM?

Some sort of positive isolation will allow you to use inert gases in vessels etc. So long as the slip or spectacle is clearly identified as Do not move or remove / MOTHBALLED written on red Tags, then I see nothing wrong.

Air gap becomes a bit harder to re commission and is lower risk, but if it's documents and marked properly the difference is small.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Mothballing - Air gap vs Blanking

LI,

I'm surprised you don't know this - I thought your background was in O&G in the USA.
PSM is USA's OSHA mandated program for "Process Safety Management of Highly Hazardous Chemicals" -29 CFR 1910.119.

Any site with above threshold quantities of toxic materials or >20,000 lbs of flammables qualifies as a PSM-covered facility, so it is a very common regulatory requirement. I know there are (or were) some exemptions in the drilling wells, but thought most O&G was covered. Perhaps I am mistaken.


MP08 - I do not know of any PSM standard that specifically address decommissioning or mothballing. You have to satisfy an auditor that you meet the requirement that the limits of the covered process are defined. Without an air gap, I am not sure if an auditor would necessarily say you were not connected to the process. One reason for doubt would be corrosion and eventual pinhole leaks in the blind causing the equipment to become "live" again. As far as I know there is no "hard" standard - it's up to the process owner to define. Hopefully the government agrees with you if that is the route you take.

RE: Mothballing - Air gap vs Blanking

Nah, It's O&G everywhere else in the world apart from the USA.... My bigger brother Big Inch was certainly involved...

PSM sounds much more like COMAH regulations in the UK and Europe.

The blind flange / spade should not be the primary barrier and hence there should be a locked off valve etc as well which helps prevent any circulation of corrosive materials. I can't recall hearing about corrosion of such taking place but there may be the odd one.

Clearly air gapping is superior to simply spading, but whether it is needed is another matter altogether.

The attached is a useful guide but doesn't have much to say about "extended isolation" as it calls it and notes that the selection tool isn't valid!

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close