Process Control High and Low Selector Usage
Process Control High and Low Selector Usage
(OP)
Hi,
I am trying to understand use of high and low selector in process control
For e.g. in the attach photo, can we use high selector for pressure and flow controller to control min. flow recycle control valve?
Should we use high or low selector?
Should PC and FC be direct acting or reverse acting?
I am trying to understand use of high and low selector in process control
For e.g. in the attach photo, can we use high selector for pressure and flow controller to control min. flow recycle control valve?
Should we use high or low selector?
Should PC and FC be direct acting or reverse acting?
RE: Process Control High and Low Selector Usage
I assume the FC is to maintain a minimum flow.
It's unusual to have both flow and pressure to maintain min flow. Why both?
But first work out what each controller is trying to control and what happens if the flow or pressure reading is higher or lower than the set point. Doe sit want to open or close the valve?
DO the two things happen together - so in this instance high pressure probably equals low flow, so in both those instances you want the valve to open.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Process Control High and Low Selector Usage
RE: Process Control High and Low Selector Usage
@hacksaw - Hydrocarbon liquid pump. normal discharge pressure is 250 psig.
RE: Process Control High and Low Selector Usage
When the process signal is lower or higher than the set point, the controller outputs a position signal to the valve positioner to either open or close to try and maintain the required set point. So as the flow through the pump increases, the flow controller wants to close the valve until it is fully closed if flow is > the min flow set point. However if the pressure is at or above the pressure set point the pressure controller wants to maintain or open further the valve. SO in this case the valve wants to have sent to it the highest value.
The position signal is what goes into the high selector block which in your case take highest position to send to the valve positioner.
For your case I can't really understand why you're doing this. A pressure signal to control low flow is much less accurate than a flow signal so why is it there?
But if you really want to do that then take both position signals and stick them into a high selector block and the valve will open more based on either lower flow than your set point OR higher pressure than your set point and flow more water of liquid around the bypass, thereby increasing flow through the pump and at the same time lowering the pressure. whichever is exceeded essentially takes control of the bypass control valve.
Does that make sense?
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Process Control High and Low Selector Usage
Most applications requiring constant process pressure with minimum flow conditions for the pump, require two valves.
RE: Process Control High and Low Selector Usage
Using a bypass line to control pressure is a poor way of doing this as it wastes a lot of energy if you want a low pressure.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Process Control High and Low Selector Usage
RE: Process Control High and Low Selector Usage
The signal is the position of the valve. So you want the highest of the two positions to be sent to the valve positioner.
Sending a low position signal would close the valve.
The control action of the valve is irrelevant here. That only affects what happens if you lose air pressure. Not connected to the control logic discussion.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Process Control High and Low Selector Usage
From your earlier comment "But if you really want to do that then take both position signals and stick them into a high selector block and the valve will open more based on either lower flow than your set point OR higher pressure than your set point and flow more water of liquid around the bypass, thereby increasing flow through the pump and at the same time lowering the pressure. whichever is exceeded essentially takes control of the bypass control valve."
so say we talk in terms of 4-20 mA signals. Since valve is fail open and air to close...more signal to the valve means it closes more and zero signal to the valve means its full open. Essentially the control valve positioner or control valve itself will have I to P converter..that will take the signal and convert it to pneumatic signal. So now if we select a high selector we are sending a higher signal from the two controllers to valve which converts to a higher pneumatic signal and closing the valve more since the valve is air to close. Hence, my confusion whether it should be a low selector or high selector.
RE: Process Control High and Low Selector Usage
From the control sketch, it looks like the pressure controller is set high, while the FC is set low.
RE: Process Control High and Low Selector Usage
The selector block might be 4 to 20 or it might be digital within the DCS.
Your final element to the valve will be reverse acting in that a 20mA signal will equal 3psi or wha tr ever is the min output pressure into the valve.
You really need to talk to a controls engineer to explain further.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.