Question on Makeup Air for hazardous Exhaust System
Question on Makeup Air for hazardous Exhaust System
(OP)
Hey everyone,
I've got a question about a piece of code from the 2018 International Mechanical Code (IMC). Section 510.6.5 states for makeup air for hazardous exhaust systems that:
Makeup air shall be provided at a rate approximately equal to the rate that air is exhausted by the hazardous exhaust system. Makeup air intakes shall be located in accordance with Section 401.4.
In addition section 501.4 on pressure equalization states that:
Mechanical exhaust systems shall be sized to remove the quantity of air required by this chapter to be exhausted. The system shall operate when air is required to be exhausted. Where mechanical exhaust is required in a room or space in other than occupancies in Group R-3 and dwelling units in Group R-2, such space shall be maintained with a neutral or negative pressure. If a greater quantity of air is supplied by a mechanical ventilating supply system than is removed by a mechanical exhaust for a room, adequate means shall be provided for the natural or mechanical exhaust of the excess air supplied. If only a mechanical exhaust system is installed for a room or if a greater quantity of air is removed by a mechanical exhaust system than is supplied by a mechanical ventilating supply system for a room, adequate makeup air shall be provided to satisfy the deficiency.
I thought that good practice concerning exhaust systems is to maintain relative negative pressure relative to spaces where the relevant air-borne hazards are lesser. When I read that makeup air shall be provided at an approximately equal rate that air is exhausted, I am not sure how it is possible to keep a space both relatively negative and where makeup air equals exhaust air. The only other way I see this making sense, is if the makeup air enters the space through an indirect system, e.g. makeup air infiltration through transfer ductwork, or through/under doors. With that interpretation you could practically rewrite section 510.6.5 to simply that "Think about where and how your air is entering your space." Any thoughts?
I've got a question about a piece of code from the 2018 International Mechanical Code (IMC). Section 510.6.5 states for makeup air for hazardous exhaust systems that:
Makeup air shall be provided at a rate approximately equal to the rate that air is exhausted by the hazardous exhaust system. Makeup air intakes shall be located in accordance with Section 401.4.
In addition section 501.4 on pressure equalization states that:
Mechanical exhaust systems shall be sized to remove the quantity of air required by this chapter to be exhausted. The system shall operate when air is required to be exhausted. Where mechanical exhaust is required in a room or space in other than occupancies in Group R-3 and dwelling units in Group R-2, such space shall be maintained with a neutral or negative pressure. If a greater quantity of air is supplied by a mechanical ventilating supply system than is removed by a mechanical exhaust for a room, adequate means shall be provided for the natural or mechanical exhaust of the excess air supplied. If only a mechanical exhaust system is installed for a room or if a greater quantity of air is removed by a mechanical exhaust system than is supplied by a mechanical ventilating supply system for a room, adequate makeup air shall be provided to satisfy the deficiency.
I thought that good practice concerning exhaust systems is to maintain relative negative pressure relative to spaces where the relevant air-borne hazards are lesser. When I read that makeup air shall be provided at an approximately equal rate that air is exhausted, I am not sure how it is possible to keep a space both relatively negative and where makeup air equals exhaust air. The only other way I see this making sense, is if the makeup air enters the space through an indirect system, e.g. makeup air infiltration through transfer ductwork, or through/under doors. With that interpretation you could practically rewrite section 510.6.5 to simply that "Think about where and how your air is entering your space." Any thoughts?
RE: Question on Makeup Air for hazardous Exhaust System
A calculation is performed per ASHRAE methods that has equations that predict the air flow across each path of the building envelope to determine the total flow at given internal space design pressure. The mechanical supply flow plus this infiltration flow though building construction will equal the exhaust air flow at the design space internal pressure. This is because at the design internal pressure you calculate the infiltration flow through the byuulding envelope, subtract this from the exhaust flow, then set you mechanical suppied air flowrate to this value.
Attached is a sample calculation from a project I worked on for negative pressurization of a space.
Note that to have a space positively pressurized you would do the opposite - set the mechanical exhaust flow lower than the mechanical supply flow with the difference flowing through the building to the outside at the desired space positive pressure (using the same pressure drop calcs from ASHRAE).