Liquid Nitrogen to Cool Condenser Water
Liquid Nitrogen to Cool Condenser Water
(OP)
During the extreme hot days of the year, our cooling towers struggle to keep the condenser water cool enough. It was mentioned that we should look into using the liquid nitrogen as well as a heat exchanger to provide additional cooling to the condenser water system. The idea is that it will both vaporize the nitrogen and cool the system. I was curious if this is even possible? I thought the temperature of the liquid nitrogen would be too cold and would cause problems more than anything. Although, I am not exactly sure. This system uses 30 percent glycol. Any help or comments is much appreciated.
Jackson Morgan
Jackson Morgan
RE: Liquid Nitrogen to Cool Condenser Water
Consider this paper issued by Praxair,
Pierre
RE: Liquid Nitrogen to Cool Condenser Water
Both the mechanical design and the thermal design are special for this service.
= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed
RE: Liquid Nitrogen to Cool Condenser Water
Rather expensive option, using LN2 for this.
Tell us about the current setup. Why not increase the exchanger surface area for the open loop CW - closed loop glycol HX instead to offset the increase fouling on the open loop CW side ?
RE: Liquid Nitrogen to Cool Condenser Water
What are the name of these exchangers? Haven't heard of them but sounds neat!
RE: Liquid Nitrogen to Cool Condenser Water
The tube pitch was fairly large because they were designed to allow significant ice formation at the cold gas inlet end.
= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed
RE: Liquid Nitrogen to Cool Condenser Water
If you're using gaseous Nitrogen from liquid for some other reason then it can make sense to use some of the cold air / liquid to help your condensor, but seems to be far too complex for only a few days a year.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Liquid Nitrogen to Cool Condenser Water
https://www.acmecryo.com/products/vaporizers/shell...
As others have said, this is a relatively expensive option unless you are already vaporizing some LN2 in your facility and this is just augmenting that.
RE: Liquid Nitrogen to Cool Condenser Water
Thank you I will take a look at those. We are already vaporizing LN2 and figured we could use this to also cool the water. Just have to figure out how much energy it would save if we used it year-round to take load off the chillers and cooling towers.
RE: Liquid Nitrogen to Cool Condenser Water
https://www.heatric.com/heat-exchangers/
RE: Liquid Nitrogen to Cool Condenser Water
@Jackson Morgan 30% glycol should make this fine. 30%vol of EG / water is around -16C for freezing point. It's about managing tube wall temperatures in the unit over your range of operating cases.
As others have mentioned, the tube pitch and overall shell diameter typically ends up larger compared to a non-cryogenic shell and tube due to allowance of ice growth. Some IG majors specify the minimum gap required (ice thickness + x mm allowance), for instance.
Assuming it is subcritical LIN you are dealing with too!