FAT for centrifugal chilled water pump

FAT for centrifugal chilled water pump

FAT for centrifugal chilled water pump

(OP)
"I Participated in a FAT (Factory Acceptance Test) for a centrifugal chilled water pump today. The tester relied on the VFD display reading to determine the RPM and kW of the motor during the test. From what I know, use a calibrated torque meter and tachometer for accuracy, and is it mandatory to get the approval from the consultant? I also noticed that the test data clearly indicates that flow will vary when the discharge valve is partially closed at different heads. Additionally, while checking the shutoff head, I observed that the valve isn't completely closed; around 230 GPM still passes through. I brought this up with the tester, and he mentioned that there's no requirement to fully close the valve. thank you in advance for your valuable response

The problem with the world is that intelligent people are full of doubts, while stupid ones are full of confidence.
-Charles Bukowski-

Replies continue below

Recommended for you

RE: FAT for centrifugal chilled water pump

What's 230 in relation to rated flow?

5% or less just means they're not stressing the pump too much.

What did the test spec say?
Is it an API 610 pump? Or some other code?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: FAT for centrifugal chilled water pump

(OP)
Sorry for typing error. The flow is not 230 GPM, but approximately 10% of the rated flow, which equates to around 50 to 60 GPM. I'll be sure to share more details about the test specifications in an upcoming update."

The problem with the world is that intelligent people are full of doubts, while stupid ones are full of confidence.
-Charles Bukowski-

RE: FAT for centrifugal chilled water pump

(OP)
@littleinch: the test code is ISO 9906 and HI-GRADE 3B. Thanks

The problem with the world is that intelligent people are full of doubts, while stupid ones are full of confidence.
-Charles Bukowski-

RE: FAT for centrifugal chilled water pump

It serves no need to test shut-off head,

It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)

RE: FAT for centrifugal chilled water pump

So what does the test code say?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close