Thank you for the responses.
I will explain the situation briefly. Currently, the condenser pump flow rate is set at 10,500 gpm with a head of 100 feet. The plant operates with three chillers, each equipped with three pumps, totaling a flow rate of 31,500 gpm. There are plans to add three more chillers, bringing the total thermal capacity to 21,000 tons. To accommodate this expansion, three additional condenser pumps with matching specifications are required.
After careful evaluation, Grundfoss pumps were selected to ensure compatibility with the existing pump, resulting in a combined flow rate of 63,000 gpm from six pumps. At this juncture, a variation was introduced by the project consultant by increasing the flow rate from 10,500 gpm to 12,000 gpm. This adjustment requires the selection of three new pumps capable of handling the higher flow rate, and the existing pumps will be upgraded by adjusting the impeller.
It's important to note that the head remains consistent at 100 feet, while the impeller size differs between the existing pumps (382 mm) and the new ones (415 mm). This change aims to provide a fail-safe mechanism in case of pump failure, ensuring uninterrupted operation. With the new configuration, the collective flow rate will be 60,000 gpm from five pumps, slightly below the previous 63,000 gpm.
However, a client has expressed questions about these changes for several reasons: client's point of view is the following,
1. The consultant's insistence on a spare pump for the condenser raises concerns, especially with six chillers already in operation.
2. Merging two hydraulic systems into a common circuit can lead to complications due to differing shutoff heads and flow rates.
3. The proposed changes could unnecessarily complicate the control system, leading to potential operational challenges.
4. Instead of the proposed approach, a more practical solution could involve stocking spare parts or an identical pump.
5. There is a discrepancy between the required flow rate (63,000 gpm) and the proposed rate (60,000 gpm with five pumps at 12,000 gpm each).
6. Increasing the flow rate to 12,000 gpm with a 600 mm inlet pipe could lead to cavitation concerns due to high velocities.
7. These concerns highlight the need for thorough analysis before implementing the proposed changes.
Your insights on this matter would be greatly appreciated.