We are adding a cooling coil to an existing commercial VAV AHU without supply air duct insulation. I am trying to calculate the minimum duct temperature that is allowable while avoiding condensation forming on the duct surface. The duct is exposed in the space and some of it is in a plenum but the system has plenum return so the air conditions should be close to what the room temperature is.
I understand there will be condensation if the duct surface temperature is at dew point temperature in the space. However, the only sources of outside air coming in the space are infiltration and the air introduced into the room from the duct (for example, near saturated 55 F air).
Thoughts? Raising the supply air temperature of the system also allows more moisture into the space which is why it's a bit confusing.
I understand there will be condensation if the duct surface temperature is at dew point temperature in the space. However, the only sources of outside air coming in the space are infiltration and the air introduced into the room from the duct (for example, near saturated 55 F air).
Thoughts? Raising the supply air temperature of the system also allows more moisture into the space which is why it's a bit confusing.
RE: Supply Air Duct Condensation Temperature
https://www.jm.com/en/hvac/duct-liner/spiracoustic...
RE: Supply Air Duct Condensation Temperature
Remember that there are other sources of water vapour in an area besides infiltration and outside air.
And typically plenum areas are warmer than room temeprature.
RE: Supply Air Duct Condensation Temperature
When you say "supply air" do you mean cool air from the AHU?
If it is why is it not insulated?
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Supply Air Duct Condensation Temperature
RE: Supply Air Duct Condensation Temperature
So, if there is a chance of condensation, insulate it. and a room could have any dewpoint... you don't know about actual use, infiltration, humans sweating etc. Our design just assumes some standard scenarios. Infiltration is a huge unknown and the climate you are in plays a huge role here. Likely not a problem in Arizona, but a huge consideration in Florida.
RE: Supply Air Duct Condensation Temperature
The ahu is serving a gym, state, and a cafeteria. The reason why we evaluating not adding insulation is because it is extremely expensive.
RE: Supply Air Duct Condensation Temperature