Mr. zaboli (Electrical)(OP)10 Jul 23 09:54
".... Should the following formula be used to calculate the voltage drop of the motor in the delta condition in a star-delta system considering that there are 2 cables between the panel and the motor and the current of this cable is 1/1.73 of the motor current?.....Should the length of the cable be considered twice?"
I look at it this way for your consideration.
1. For simplicity, take the motor (run/delta) or rated current be I A.
2. A SD starter, when in run/delta condition:
a) the source current is I A.
b) the current flow through the main contactor = the delta contactor= the current flow through each of the six conductors.
c) the current is [ 0.732 x I] A.
3. The VD is calculated based on the current above 2. c).
4. For simplicity, the pf may be taken as 1.0, instead of the rated; as it varies within a small range, depending on the load.
Che Kuan Yau (Singapore)