Penetration through composite steel decking and concrete

Penetration through composite steel decking and concrete

Penetration through composite steel decking and concrete

(OP)
During the renovation of a 20th story high-rise residential unit, it became necessary for a medium sized 28"X36" hole to be cut in the floor to perform a plumbing tie-in when the lower floor was inaccessible. The area of this floor will never be exposed to significant loads beyond a residential use.

The building is a 1980's vintage, 30 story steel building with concrete floors poured over traditional composite steel decking. The slab thickness varies from 7" to 5" depending on the area of the pan's corrugation.

I have found lots of guidance from Hilti as well as other resources that cover penetrations through this flooring type, but all assume the opening will remain permanent and the engineering measures to be taken assume this. In this case, the opening is to be closed once the access is no longer needed. Aside from placing a remnant of composite decking as a form, screwed to the overlap of the penetration, doweling and epoxying rebar on similar centers in to the concrete, placing like-kind mesh, and repouring the concrete, should any other reinforcing measures be taken?

Regards,
An appreciative new member.
Replies continue below

Recommended for you

RE: Penetration through composite steel decking and concrete

My concern with what you've proposed is that:

1) I assume that the original deck was meant to be the tension reinforcement for the slab AND;

2) I don't feel that nominally screwing the deck remnant thing back in there restores that.

Any chance you could expand the opening to the nearest deck supports and then infill that with tension rebar where you need it?

Of course, treating the thing as a permanent opening, even with the opening, remains an option if that's the easier path.

RE: Penetration through composite steel decking and concrete

Would it not be possible to puddle weld the new decking on to the existing decking from underneath? Following the manu. specs for puddle welds.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close