Contact US
the quality of valve manufactures
What is the industry's quality experience with Siemens valves such as butterfly, globe, and control valves? In one of my 13-year-old buildings with centrifugal chilled water systems, I observed that almost all of the Siemens motorized isolation butterfly valves are not sitting properly when they receive signals to close chilled and condenser water. Water can flow through 5 to 10% of the openings. Almost all Siemens valves behave in this manner. As a result, it was an operational failure. The BMS system has been improved, and a valve maintenance plan has been developed. One valve was disassembled and dismantled. However, the valve disc is rusted, and the disc side is damaged, which I believe is due to cavitation. Because it is a small percentage, it is constantly open, even when the power is turned off. Cavitation will happen. My question is concerning the dependability of valve manufacturers. When purchasing valves, it is normally advisable to go to the original manufacturers whose major business is producing valves, with the exception of Siemens and Honeywell, which do not have factories that produce valves and instead have valves built for them by third-party Chinese firms. This is being discussed in the industry. I don't know anything else about it. Is this taken into account when ordering valves, particularly for major projects? What is your professional opinion? Thank you for any feedback.
The problem with the world is that intelligent people are full of doubts, while stupid ones are full of confidence.
-Charles Bukowski-
RE: the quality of valve manufactures
This is not a quality issue. It is a combination of incorrect trim specification and/or poor water treatment. A stainless steel or bronze disc should have been specified for this application.
Good day,
Been in valve industry for 20 years, I barely have any experience with Siemens. So cannot say they are bad or good.
It is quite common in certain system and/or skid to buy a bundle of equipment from single source supplier, so let say we buy Flowserve pump, then skid components (valve, etc.) surrounding it will be kind of black box for end user. Not necessarily for example the ½” – 150# ball valve supplied by them will have inferior quality (FS don’t make small, relatively low engineering ball valve).
Before jumping to quality of certain (not commonly known as) valve supplier, would suggest performing more elaborative root cause analysis:
-What sort of butterfly valve? Metal seated triple offset or rubber seated double or even zero offset.
-If replaceable rubber seat butterfly valve, then who installed it? Please note that this kind of valve should be in open position during flange tightening. Risk (tightened in close position) will make the seat bulging, and block valve movement. Eventually will torn the seat as well.
-Motorized valve got stuck at 5% when signal given is 0% (fully close) ? Isn’t this going to trigger some alarm? What sort of response did you do e.g. manual override it, increase the torque, etc.?
-What material is the disc/seat? Did Siemens specify the material or is this the End user part?
-Pitting corrosion remarks in comparison with cavitation can be quite subtle for common eyes. Is your cavitation theory has been verified by metallurgist?
-Corrosion on disc usually not causing valve to get stuck. Stuck on butterfly valve is more corrosion on bottom/top bearing and or bulging on rubber seat
Agree with TugboatEng, the contributing factors can be design and material specifications issue.
Please note that it is harder and more expensive to find pure metal ore. By that respect for the last 10+ years, we are already entering the era of renewable metal, which has lower nickel and molybdenum content. More susceptible to pitting corrosion.
Excuse my grammar.
D
@ TugboatEng: thank sir for the response. A third-party contractor routinely treats the chilled water system. According to my understanding, the trim specification relates to the internal condition of the valve. In this instance, however, the valve is not closing properly; rather than a single valve, six valves are functioning identically in the same plant room. Overriding the disc and closing down are ineffective. What I've found is that the problem is mechanically and not related to the actuator. Recently, it was sent to an outside service, where the defects were rectified. However, because the near-closed operation may cause cavitation, the side of the disc has already corroded with pits. I classified it as a manufacturing defect for this reason.
Is it true that Siemens does not have a factory to produce its own brand of valves?
-Charles Bukowski-
@Danlap, Thanks for taking time to explain more about it.the datasheet for the concerned valve is attached. The specification is not shown as a triple or zero offset. The identical valve proposed for a new project for the motorised isolation purpose for the plate heat exchanger! I came upon the identical info sheet. “The project consultant advises that the butterfly valve in the ETS room be double eccentric." I reviewed the datasheet for the exact word; it is not listed.
“Pitting corrosion remarks in comparison with cavitation can be quite subtle for common eyes. Is your cavitation theory has been verified by metallurgist?
There is no third-party confirmation; I assumed it was cavitation.
-Charles Bukowski-
Hello moideen,
This is a classical example : everything is OK but the end result. As mentioned by others (I do agre with the posts above) several things might be wrong. With stainless steel as spcified for the disc, it is more likely that the pistting is cavitation corrosion. This should however be easy to spot for engineers familiar with cavity damage by the cavitations 'non smooth' pitting grooves, and likely similar damage for all six valves.
Further, if we assume cavitation, it could be mannufacturing faults (outside tolerence limits for disc, sealing or positioning), but most common are unprecise adjustments of actuators limit switches.
I doubt that a well renowned German company as Siemens could have slipped on product quality control, and would suspect bad adjustment of control devices/limit switches and/or false mounting/support for the valves with actuators.
The mechanical faults mentioned I would have liked more specified, with photos of damage and pipeline installations.
As mentioned lugged or flanged valves with double eccentric closing would have been better. As a tip for this size of valves, closing and opening time can often be doubled (or more) giving smaller elecrtical actuaters with gear, at lower total cost.
Good luck with your investigations!
Don't get me started on ZF azimuthing thrusters... Country of origin is not a determination of quality.
TugboatEng, You caught me there....I stand corrected!
Click Here to join Eng-Tips and talk with other members! Already a Member? Login
Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now
Close Box
Join Eng-Tips® Today!
Join Us             Close