Hello,
For a CT installed indoors in a powerhouse, what is the "typical" or rule-of-thumb life cycle of a CT? What are factors affecting the life expectancy and is it common to see a CT fail in service? Typically, CT's are not maintained, so I was wondering what could be leading up to a failure..
My understanding is that CT's, especially older CT's could last 70 years or more.
Your thoughts are appreciated.
Thanks,
EE

RE: Life expectancy of a current transformer

I’ve not seen a CT fail due to age yet. We have CTs that are 64 years old and still in service.

RE: Life expectancy of a current transformer

I just finished a project where one of the buildings had a line up of 15kV metal clad switchgear that was installed in 1954. The breakers had been retrofitted as well as the relaying. It was a damp, poorly heated building. I spoke with the relay tech that was involved in the upgrade a few years ago. They evaluated the CT's with fairly standard tests including, ratio, polarity, excitation and megger. All of the original CT's were deemed ok for reuse. There were 26 breaker cubicle with line and bus dif CT's.

Outside in the switchyard, slip over CT's had been installed 20 years ago for a metering application that never happened. The CT's were shorted at the terminal block. I noticed the CT's were cracked and some were dripping rusty water. We had those CT's removed. This is a northern climate that gets snow and ice.

In my experience, CT's don't fail all that often. I've tested thousands and I can distinctly remember the 2 that were real fails, as they were installed inside large transformers. More often it's wiring and connections. Leave a CT open and it will fail.

I suppose some things that could lead to premature failure would include caustic environment, high temperatures, constant vibration and thermal cycling. If the CT is in metal clad switchgear, it's probably pretty safe. Same for inside a breaker or transformer. I suppose a bar type not rated for and subjected to multiple through faults could fail.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close